twofer said:
nofossil said:
Here's a simple schematic showing on possible way to do it. The number of connections depends on the tank, but the important idea is that you want maximum startification - hottest water at the top.
But it seems like if the boiler isn't running then you're taking cold water off the bottom of the tank and then dumping on the top before it gets sent to the zones. I'm having a heck of a time wrapping my head around this.
In the system I posted, think of it this way:
- There are three circulators, each with a check valve to prevent reverse flow.
- If there's heat demand, the secondary loop circ (on the right) runs, drawing hot water from the top of the tanks, pushing it through the zone(s), and returning it to the bottom of the tanks.
- If either boiler is operating, the circ for that boiler is on, drawing water from the bottom of the tanks, heating it, and returning it to the top of the tanks.
- If a boiler is not operating, there is NO flow through that boiler.
If a boiler is operating AND one or more zones is calling for heat, then a boiler circ and the secondary loop circ will both run. Depending on the relative flow rates, you may get excess hot water from a boiler going into the top of the tanks as well as feeding the secondary loop. You might also get no flow in or out of the tanks.
The idea is that the tanks isolate the control logic. Zone demand simply turns on the secondary circ. An operating boiler simply turns on its own circ.
The only additional logic that you might need is an aquastat that turns on the oil boiler if there is demand and the top of the storage is not hot enough.
Standing tanks on end would probably improve stratification, but I think that legs and fittings are arranged so that horizontal mounting is easier.