Using the VERY helpful document from TACO below, it looks like I need a Taco 0013. I'm running 1.25 PEX about 180' from boiler to heat exchanger. I have a Biomass 60, 200kbtu boiler. It looks like my head loss is in the 22-24 feet range and it looks like I need about 17 gpm to get 170kbtu to the house. I'd like to order the pump today and I'm wondering if this passes the sniff test to you guys.
(broken link removed to http://www.taco-hvac.com/tmp/SelectingCirculators.pdf)
Also, I thought I posted a question yesterday about why some of you talk about putting a sensor line in the trench. I'll be covering up my trench and if that is something I useful I'll get one. But I don't know what it would be used for. The boiler works off the return water temp so why would I need sensor data from the house??
I'd really appreciate input from you experts if the pump sounds right. Per the tables it does, but I'd feel better to hear from an experienced user. Thanks
(broken link removed to http://www.taco-hvac.com/tmp/SelectingCirculators.pdf)
Also, I thought I posted a question yesterday about why some of you talk about putting a sensor line in the trench. I'll be covering up my trench and if that is something I useful I'll get one. But I don't know what it would be used for. The boiler works off the return water temp so why would I need sensor data from the house??
I'd really appreciate input from you experts if the pump sounds right. Per the tables it does, but I'd feel better to hear from an experienced user. Thanks