Working on this Quad Contour. I did a little rewire because I did not like the fuse.
https://www.hearth.com/talk/threads/well-it-is-time-to-re-wire-this-old-aladdin-quadrafire.128671/
The stove fires and starts feeding pellets when the T-Stat terminals are jumped.
Tried cleaning the thermocouple cover but still did not work. Also changed control boxes and still did not work.
Could it be a bad thermocouple? Any good way to test? How many millivolts should it read with a flame present?
I heard if you pull the Thermocouple cover off and put a flame under it, then a meter should read 15 - 18 Millivolts?
See pics below. Click pics to enlarge:
Working on this Quad Contour. I did a little rewire because I did not like the fuse.
https://www.hearth.com/talk/threads/well-it-is-time-to-re-wire-this-old-aladdin-quadrafire.128671/
The stove fires and starts feeding pellets when the T-Stat terminals are jumped.
Tried cleaning the thermocouple cover but still did not work. Also changed control boxes and still did not work.
Could it be a bad thermocouple? Any good way to test? How many millivolts should it read with a flame present?
I heard if you pull the Thermocouple cover off and put a flame under it, then a meter should read 15 - 18 Millivolts?