well, this summer I decided to try my hand at a DIY install of AtticFoil (http://www.atticfoil.com/) over the attic floor. it's perforated so it doesn't provide a complete moisture barrier (important for attic floor installs) although I'm not sure how much that matters for me b/c my attic has boards nailed down over most of the surface, but anyhow I've done measurements with an IR thermometer to see if the stuff's just a gimmick or does anything and I gotta say, it's not bad.
a rough apples-to-apples comparison in the summertime:
5/3/2010 - pre-atticfoil install - outside temp ~92F, A/C was running at around 82% duty cycle with the thermostat set at 76F.
8/8/2010 - post-atticfoil install - outside temp ~90F, A/C was running at 58% duty cycle with the thermostat set at 76F.
both days were sunny and clear.
using the IR thermometer, I took a few example readings in the attic.
8/8/2010 - outside temp ~90F, roofing boards 130F, attic floor underneath foil is at 105F
8/21/2010 - outside temp ~77F, roofing boards 110F, attic floor underneath foil is at 86F
on the cooler side:
9/15/2010 - (7AM) outside temp ~53F, roofing boards 53F, attic floor underneath foil is at 60F
9/16/2010 - (7PM) outside temp ~65F, roofing boards 70F, attic floor underneath foil is at 75F
FYI I did try pointing the IR thermometer at the attic foil from above, usually I get the same reading as the roofing boards within +-1F or so.
Very interested to see how this changes things in colder <30F weather. I know that in really cold sub-25F weather around here a firing of my VC Defiant with 6 woodbrickfuel + 1 slat of pallet wood yields a ~12F increase in thermostat reading around 3hrs after ignition, and a fire started around 9-10PM will keep the heat pump from kicking on until ~3-4AM (thermostat set at 70F) for an average 3degF/hr drop in temperature off the peak so I'll use that as a basis for comparison.
Beyond the foil, my attic has fiberglass batts up to the ceiling joist height with boards over most of the attic except some spots. I've covered the attic floor as best as I could, overlapping the sheets where necessary.
as for cost, I bought the foil in 500sqft increments (thought I only needed 500sqft based on a rough measurement of the attic, but turns out I was wrong and there was some overlapping I didn't consider) and ended up buying 2 of them, each roll cost ~$84 shipped so I blew ~$168 on the project. the site claims it qualifies for the 30% tax credit so I'll look into that come tax time. not too pricey at all! I still have most of the second 500sqft roll left too for any fun projects I dream up involving the stuff ... lol
a rough apples-to-apples comparison in the summertime:
5/3/2010 - pre-atticfoil install - outside temp ~92F, A/C was running at around 82% duty cycle with the thermostat set at 76F.
8/8/2010 - post-atticfoil install - outside temp ~90F, A/C was running at 58% duty cycle with the thermostat set at 76F.
both days were sunny and clear.
using the IR thermometer, I took a few example readings in the attic.
8/8/2010 - outside temp ~90F, roofing boards 130F, attic floor underneath foil is at 105F
8/21/2010 - outside temp ~77F, roofing boards 110F, attic floor underneath foil is at 86F
on the cooler side:
9/15/2010 - (7AM) outside temp ~53F, roofing boards 53F, attic floor underneath foil is at 60F
9/16/2010 - (7PM) outside temp ~65F, roofing boards 70F, attic floor underneath foil is at 75F
FYI I did try pointing the IR thermometer at the attic foil from above, usually I get the same reading as the roofing boards within +-1F or so.
Very interested to see how this changes things in colder <30F weather. I know that in really cold sub-25F weather around here a firing of my VC Defiant with 6 woodbrickfuel + 1 slat of pallet wood yields a ~12F increase in thermostat reading around 3hrs after ignition, and a fire started around 9-10PM will keep the heat pump from kicking on until ~3-4AM (thermostat set at 70F) for an average 3degF/hr drop in temperature off the peak so I'll use that as a basis for comparison.
Beyond the foil, my attic has fiberglass batts up to the ceiling joist height with boards over most of the attic except some spots. I've covered the attic floor as best as I could, overlapping the sheets where necessary.
as for cost, I bought the foil in 500sqft increments (thought I only needed 500sqft based on a rough measurement of the attic, but turns out I was wrong and there was some overlapping I didn't consider) and ended up buying 2 of them, each roll cost ~$84 shipped so I blew ~$168 on the project. the site claims it qualifies for the 30% tax credit so I'll look into that come tax time. not too pricey at all! I still have most of the second 500sqft roll left too for any fun projects I dream up involving the stuff ... lol