Sad, this is like one of those 'find 10 things wrong with this picture'. The good news is that you had the wisdom to ask for help.

It's a tear-out. In the end it could be that only the stove pipe is saveable.
 
Its not a good situation, but your alertness caught the error, good luck with getting it corrected.
 
Thank goodness and the Lord no one was hurt, this can be fixed. Like your stove too. Good luck.
 
I’d say you’re EXTREMELY LUCKY nothing bad has happened. I would 100% take this man to small claims court if he didn’t give me every cent of my money back (minus the stove price).
 
Yes, we are quite thankful to the Lord that nothing bad happened! Stovepipes can be fixed, and money is replaceable. The inspector checked it out this morning and flagged everything that's been mentioned here, plus he said that the cap is wrong for a wood stove, being the style intended for a gas furnace. (The slots are too small for wood, and will plug up.) Between parts and labor, he estimates it will be about $2K to fix the situation. Ironically, he thinks the installer's misuse of insulation is probably what saved the roof opening from leaking this spring.

Small silver lining: The inspector (who will also be doing the repair) thinks we are safe to bend the 10-3-2 rule in this particular case, because the chimney is on the west side of the roof and the prevailing wind here is from that direction. He thinks it would be a problem if it were on the east slope, but since it is where it is and has a history of drawing just fine, we're safe to leave it the same height.

I have reached out to the installer, who is at this point unrepentant. Even in the face of photo evidence, he insists that the B-vent is actually Class A chimney, and he also persists in the belief that fire-rated spray foam is acceptable to be in contact with the pipe. (This also despite pics of the scorched and melted foam.) He has requested a copy of the inspector's formal report, which I told him I will happily share.
 
So I'm doing a little brainstorming, trying to get ahead of this and mitigate the cost of materials. My installer will verify if this is the right pipe, but does anyone have any thoughts on the following Marketplace listing? The seller has agreed to $100 for (2) 4' sections, which I think is what I'll need. I think that is a really good price, but how does the condition look to you?
 
Pass. It's old style, galvalume, wrong parts, and more than you need. We have no idea how a used chimney pipe was treated, but if it is Simpson Duratech, then it's about 20 yrs old.

Do it right. If there is a Menards in the area, they have good pricing on Selkirk chimney pipe. A good, metal roof flashing may need to be ordered separately.

www.woodstovepro.com has decent pricing if ordering online.
 
  • Like
Reactions: webby3650
Yes, we are quite thankful to the Lord that nothing bad happened! Stovepipes can be fixed, and money is replaceable. The inspector checked it out this morning and flagged everything that's been mentioned here, plus he said that the cap is wrong for a wood stove, being the style intended for a gas furnace. (The slots are too small for wood, and will plug up.) Between parts and labor, he estimates it will be about $2K to fix the situation. Ironically, he thinks the installer's misuse of insulation is probably what saved the roof opening from leaking this spring.

Small silver lining: The inspector (who will also be doing the repair) thinks we are safe to bend the 10-3-2 rule in this particular case, because the chimney is on the west side of the roof and the prevailing wind here is from that direction. He thinks it would be a problem if it were on the east slope, but since it is where it is and has a history of drawing just fine, we're safe to leave it the same height.

I have reached out to the installer, who is at this point unrepentant. Even in the face of photo evidence, he insists that the B-vent is actually Class A chimney, and he also persists in the belief that fire-rated spray foam is acceptable to be in contact with the pipe. (This also despite pics of the scorched and melted foam.) He has requested a copy of the inspector's formal report, which I told him I will happily share.
If he doesn’t think the 10-2-3 rule applies in your situation, how can you trust him as a professional? This is code..
 
  • Like
Reactions: bholler
If he doesn’t think the 10-2-3 rule applies in your situation, how can you trust him as a professional? This is code..
There is no code in our county, so there's some flexibility. He's been in this business locally for 45 years, so I would give a fair amount of credibility to what he says. Also, code or not, nobody has told me what actual difference that makes as long as the stove is drafting properly (it is) and the roof is metal (not prone to ignite). Seems more like checking a box that doesn't make any real-world difference in my case.
 
Pass. It's old style, galvalume, wrong parts, and more than you need. We have no idea how a used chimney pipe was treated, but if it is Simpson Duratech, then it's about 20 yrs old.

Do it right. If there is a Menards in the area, they have good pricing on Selkirk chimney pipe. A good, metal roof flashing may need to be ordered separately.

www.woodstovepro.com has decent pricing if ordering online.
20 years old? How does that follow? You can buy this particular item (Duravent 9407GA) online today: https://woodstovepro.com/chimney-pi...ObmcJKFu-DZ85nCx76hb2_uGiwDz09RV_nvUooTAk3-rh

Also there is more than I need, but that's why I'd only be buying (2) 4' sections. At $100 for both, that's a pretty good deal.
 
There is no code in our county, so there's some flexibility. He's been in this business locally for 45 years, so I would give a fair amount of credibility to what he says. Also, code or not, nobody has told me what actual difference that makes as long as the stove is drafting properly (it is) and the roof is metal (not prone to ignite). Seems more like checking a box that doesn't make any real-world difference in my case.
The code is an international code. It applies everywhere, unfortunately it’s not enforced everywhere. You are in an area that’s not inspected unfortunately. This would have been avoided if codes were enforced in your area, and the installer would be liable.
 
  • Like
Reactions: bholler
There is no code in our county, so there's some flexibility. He's been in this business locally for 45 years, so I would give a fair amount of credibility to what he says. Also, code or not, nobody has told me what actual difference that makes as long as the stove is drafting properly (it is) and the roof is metal (not prone to ignite). Seems more like checking a box that doesn't make any real-world difference in my case.
Yes there is code in your county. There might not be code inspectors but there is still code that needs to be followed. It looks like your already on the short side for your chimney just do it right.