Pagey said:What's behind the brick? Standard 2x4s?
Edthedawg said:Brick wall facing wood studs isn't considered protection in and of itself. It's non-combustible, yes, but an unprotected surface per NFPA 211. You will want to pay very close attention to how your manual calls out clearances - you will likely not be able to reduce clearance w/out adding protection (i.e. air-space).
What kind of stove is going in here?
And while we're at it - am I reading this correctly that there are two brick walls back to back w/ that fireplace(?) in between? Tells me there could be a large masonry chimney plunked thru the middle of the house there - not stud walls? I see the old thimble blocked off - multiple flues do exist? Or this install is going to add a new pre-fab chimney parallel to the existing one? I'm kinda wondering if the true construction is really known here.
If it's all masonry back there, your worries ease significantly...
Pagey said:I'm confused now. If you are using the existing masonry chimney, then why are you considering the clearances and double wall pipe? Wouldn't you be looking at a stainless steel liner for the existing chimney?
BeGreen said:I also think there's a good chance that this is an all masonry structure, with some rubble fill. You might try a couple exploratory pilot holes behind the stove area or actually try to remove a brick if unsure. But given the Endeavor's 4.25" clearance to combustibles when installed with double-wall pipe, this seems like a non-issue. Even if you place the back of the stove 4.25" away from the brick and there is wood behind it, the stove back is still over 7" from the wood. Just be sure the flue is the right size, certified to be in good condition and cleaned.
We use essential cookies to make this site work, and optional cookies to enhance your experience.