Hello,
I have been a lurker for some time here. I have always wanted to use wood (or the option of coal) as a supplemental heating source. I recently ordered a Royall 6150 indoor boiler for my home to tie into my existing system.
I recently moved into a 2570 square foot home. 2x6 construction, insulated walls, attic, and the ceiling of the basement is insulated between the joists. It is a two story colonial of 2003 construction. Located in central Connecticut. I would define it as being a well insulated home. I am not planning on running thermal storage, but open to the possibility at a later time. I also may end up heating my basement and garage, which would add about 1500 square feet (potential maximum of 4000 square feet heating space).
I have a fear this boiler may be oversized. Royall states this boiler can heat up to 3000 square feet. I did a heating calculation (assuming I did it correctly) the heat loss came out to about 53,000 BTU/hr. I also plan to use this boiler for my DHW needs, which I know adds some heat load to that.
I brought this concern to Royall and the sales rep states their boilers are rated at half of an equivalent gas fired unit. Meaning a 150K BTU model is equivalent to a 75K BTU propane or natural gas boiler. He also stated I'm better off going a little bigger as to increase burn times.
Does this make any sense? As far as I'm concerned, an output BTU is an output BTU. Then there is the aspect of output BTUs over 8/12 hours, as wood is not a constant heat source. Perhaps that is what is eluding to. I also understand the rated output is based on a perfect burn condition at a single point in time.
For reference, my current system is hot water baseboard, 80% efficient oil fired boiler with tankless coil for DHW. It is rated at 175K input, 144K output, and 123K net IBR output BTUs. To me it seems a bit oversized, but I haven't lived with it through a winter yet to really know for sure. The previous owners stated they burned about 1200 gallons of oil a year.
Thoughts?
I have been a lurker for some time here. I have always wanted to use wood (or the option of coal) as a supplemental heating source. I recently ordered a Royall 6150 indoor boiler for my home to tie into my existing system.
I recently moved into a 2570 square foot home. 2x6 construction, insulated walls, attic, and the ceiling of the basement is insulated between the joists. It is a two story colonial of 2003 construction. Located in central Connecticut. I would define it as being a well insulated home. I am not planning on running thermal storage, but open to the possibility at a later time. I also may end up heating my basement and garage, which would add about 1500 square feet (potential maximum of 4000 square feet heating space).
I have a fear this boiler may be oversized. Royall states this boiler can heat up to 3000 square feet. I did a heating calculation (assuming I did it correctly) the heat loss came out to about 53,000 BTU/hr. I also plan to use this boiler for my DHW needs, which I know adds some heat load to that.
I brought this concern to Royall and the sales rep states their boilers are rated at half of an equivalent gas fired unit. Meaning a 150K BTU model is equivalent to a 75K BTU propane or natural gas boiler. He also stated I'm better off going a little bigger as to increase burn times.
Does this make any sense? As far as I'm concerned, an output BTU is an output BTU. Then there is the aspect of output BTUs over 8/12 hours, as wood is not a constant heat source. Perhaps that is what is eluding to. I also understand the rated output is based on a perfect burn condition at a single point in time.
For reference, my current system is hot water baseboard, 80% efficient oil fired boiler with tankless coil for DHW. It is rated at 175K input, 144K output, and 123K net IBR output BTUs. To me it seems a bit oversized, but I haven't lived with it through a winter yet to really know for sure. The previous owners stated they burned about 1200 gallons of oil a year.
Thoughts?