Running PelPro PP130 from a generator

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.

cja7928

New Member
Feb 11, 2023
3
Emmett ID
I recently purchased a PelPro PP130 pellet stove which I need to be able to run from a backup generator. I’ve reviewed a fair amount of info online regarding people running their stoves from small generators and didn’t expect it would be a problem. I bought a Honda EU1000i inverter generator and plugged it into my stove and found the stoves controls indicators seem to function as normal, the igniter works fine and lights the pot, but the exhaust blower barely turns and the auger never comes on. When I plug the stove into the house it works fine. The stove is pulling 315 watts during startup and 127 watts during normal operation. The generator outputs 900 watts and has plenty of juice to run the stove, not to mention I’ve run my entire house HVAC off the same generator with no issues, but with only the PelPro plugged into the generator on both eco and full modes the exhaust blower barely functions. I contacted PelPro customer support and explained the situation, I told them it’s the only thing running off the generator; they came back with telling me they don’t test their products to see if they will run from generators and I needed to make sure I’m not running multiple appliances and that my generator probably doesn’t have enough power – zero effort and no interest in helping me, I pushed back asking for some technical resources but they were not willing to help. Has anyone ever experienced an issue like this? Ive seen several people powering their stoves from generators and I’m wondering If there is just something about PelPro stoves, or the control board that doesn’t like the generator frequency? Perhaps I need a different generator or some type of signal conditioner? It seems strange to me that they would manufacture a stove that’s not capable of being powered from a generator and what the issue could be?
 

Mt Bob

Minister of Fire
Oct 31, 2013
4,422
park county montana
Yes, some stoves do not want to run on a generator. You can try a few things, try a regular, non inverter generator. Grab a UPS for a PC, see if it will run on the battery, when unplugged from wall. If does, try plugging the UPS into the inverter gen.
 

cja7928

New Member
Feb 11, 2023
3
Emmett ID
Yes, some stoves do not want to run on a generator. You can try a few things, try a regular, non inverter generator. Grab a UPS for a PC, see if it will run on the battery, when unplugged from wall. If does, try plugging the UPS into the inverter gen.
Thank you. I'll try ordering a UPS and see how that works.
 

Jeremy6500

Feeling the Heat
Jan 22, 2021
360
Indiana
I have a pp130 and run it off my 2500 watt inverter generator with no issues. I run the stove and a few other things at the same time.

I guess it is possible there is a generator power issue, but it sounds odd. Motors such as fans and compressors take a surge to start. Maybe that is what is causing it.
 
  • Like
Reactions: VintageGal

gfreek

Minister of Fire
Nov 5, 2010
1,694
WNYS
I thought there was another PelPro owner here that had the same issue , not being able to run off a generator.. Can't find it though..
 

cja7928

New Member
Feb 11, 2023
3
Emmett ID
So I bought a fairly decent Cyber Power UPS and it does the same thing, wont run the blower or auger. Given the stove is just a couple blower motors and an auger I don't see how they figured out how to make it not run from a generator (or UPS), must be something with how they designed the control board. This Pelpro stove is more or less junk if it cant be used on a backup. It would be nice if there was more info out there letting people know Pelpro stoves wont run from a generators. I might just gut the Pelpro control board, hardwire the blowers and setup my own timer for the auger - probably be more reliable given how much Ive read about the Pelpro boards going out.
 

Canadianchill

New Member
Oct 3, 2022
12
Ontario Canada
I have a PP90, and have it plugged into a UPS also, mainly because I want a controlled shutdown if power fails. The stove runs fine on the UPS alone.
I have never tried running on a generator, but I will try that this weekend.
If the stove works on the UPS, I see no reason why it wouldnt run if you feed the gen power to the UPS.
I will let you know how it works out.
 
  • Like
Reactions: Mt Bob

gfreek

Minister of Fire
Nov 5, 2010
1,694
WNYS
So I bought a fairly decent Cyber Power UPS and it does the same thing, wont run the blower or auger. Given the stove is just a couple blower motors and an auger I don't see how they figured out how to make it not run from a generator (or UPS), must be something with how they designed the control board. This Pelpro stove is more or less junk if it cant be used on a backup. It would be nice if there was more info out there letting people know Pelpro stoves wont run from a generators. I might just gut the Pelpro control board, hardwire the blowers and setup my own timer for the auger - probably be more reliable given how much Ive read about the Pelpro boards going out.
So while stove is running, plugged into the UPS, if you unplug the UPS from the outlet it won't continue to run ?? Spec shows 2.3 amps running, 276-300 watts.
This is in the owners manual, weird..
"This Stove needs 110v to run properly. This Stove has not been tested for use with a third party battery backup"
 
Last edited:
  • Like
Reactions: Mt Bob