Storage does two things:
- Absorb excess heat while the boiler is operating. This allows the boiler to run at peak efficiency without idling.
- Provide heat to the heated space, DHW, and/or other destinations when the boiler is not operating.
Pretty straightforward, yes? The devil is in the details.....
In order to accomplish mission number 1 above, the storage system MUST provide return water that's cool enough to keep the boiler loaded. If the boiler is set for a maximum outlet of 180
and provides a 20
rise, then return water must be below 160
to prevent idling. For storage to be effective at absorbing heat, it must return relatively cool water as long as possible. If proper stratification can be maintained, it's possible to push hot water into the top above a layer of cool water that gets gradually pushed down. This allows the boiler to run at peak output until storage is completely charged.
For mission #2 above, it's desirable for storage to provide water that's as hot as possible for as long as possible. Ideally, water would be drawn from the top of storage at a high temp - say 180
, and returned at a very low temp - say 100
. If stratification is maintained, you can be drawing very hot water right to the point where the tank is completely discharged. To get a huge delta T like this requires a lot of thought (and likely a radiant slab), but it's by far the most effective way to use storage.
Think of it this way: a tank that has 500 gallons of water in the top half at 180
and 500 gallons in the bottom half at 120
is much more useful for either absorbing heat or providing heat than a tank that's 150
top-to-bottom, even though they both have the same amount of BTUs.