This might be interesting to some. The following chart shows data from operation of my Tarm yesterday.
Data: As with all data, it's only as good as the inputs. All water temperature readings are taken with probe milk frothing thermometers zip tied to the pipes and then wrapped with insulation. Before using the thermometers, I placed all of them on the same heat source and then adjusted them so that they all read the same, my way of calibrating them. I don't know absolutely how accurate they are. A Rutland probe thermometer is in the flue.
The 8 gpm for the boiler loop is taken from the Taco 009 pump curve chart and is assumed, as total head is estimated to be 5-10 feet. The 7.5 gpm on the system loop is calculated based on measured flow with a flowmeter reading 5.8 gpm, which has about a 2 psi pressure drop, and then operating the circulator without the flowmeter which achieves about a 4.6 foot decrease in head. Maximum gpm's for a 009 is about 8.
System: Tarm Solo Plus 40 with 50% antifreeze. Plate HX 5 x 12 x 30 plate; boiler:1.25 copper to 1.00 copper. System heat load is 100% to pressurized storage, 1000 gal.; 1.00 copper to 3/4 pipe.
Test: The boiler was cold started. An aquastat on the boiler return line after the Termovar is set to ON at 155F. This turns on both the boiler and system circulators at the same time. Since the aquastat is fed by gravity flow, when it turns ON, the top of boiler water temperature actually is greater than 155F.
Temperature readings were taken every 10 minutes during an ON or OFF cycle.
Example: At 12:31 the aqustat turned on both circs. This first ON cycle was 76 minutes long before the boiler cycled off. Boiler water input to the HX was 170 and HX return to boiler was 130. The return to boiler after the Termovar was 148, which meant that the Termovar was mixing some boiler output directly back to boiler return. Boiler side BTU's were BOILER INPUT TO HX - BOILER RETURN (deltaT) X 8 gpm x 500 x 0.85. The 0.85 factor relates to 50% antifreeze solution, which has about 85% of the heat capacity of water at 160F.
On the system side, tank input to the HX was 130 and HX output to the tank was 145. System side BTU's were HX OUTPUT TO TANK - TANK INPUT TO HX X 7.5 gpm x 500.
Note: in this first entry BTU's available on the boiler side were 70,400 but that BTU's extracted by the HX were 56,250, for an 80% transfer efficiency. Note also that as system input temperature rises, HX heat transfer efficiency decreases.
Note: that as system input temp rises, the boiler starts to cycle through idle periods. With the given gpm's and HX specs, the system side cannot keep up with boiler output as system temp rises. More gpm's and/or a larger HX would reduce cycling.
Note: if water rather than antifreeze were used in the boiler loop, boiler BTU output to HX would increase by about 18%, and HX output to system also would rise adjusted by the heat transfer efficiency.
Other: the data is what it is. I don't think I made any errors. Obviously, to the extent that temp readings are inaccurate, or gpm's are inaccurate, the BTU calculations will not be accurate.
Have fun for this if it makes any sense to you. Ask questions if you wish.
Data: As with all data, it's only as good as the inputs. All water temperature readings are taken with probe milk frothing thermometers zip tied to the pipes and then wrapped with insulation. Before using the thermometers, I placed all of them on the same heat source and then adjusted them so that they all read the same, my way of calibrating them. I don't know absolutely how accurate they are. A Rutland probe thermometer is in the flue.
The 8 gpm for the boiler loop is taken from the Taco 009 pump curve chart and is assumed, as total head is estimated to be 5-10 feet. The 7.5 gpm on the system loop is calculated based on measured flow with a flowmeter reading 5.8 gpm, which has about a 2 psi pressure drop, and then operating the circulator without the flowmeter which achieves about a 4.6 foot decrease in head. Maximum gpm's for a 009 is about 8.
System: Tarm Solo Plus 40 with 50% antifreeze. Plate HX 5 x 12 x 30 plate; boiler:1.25 copper to 1.00 copper. System heat load is 100% to pressurized storage, 1000 gal.; 1.00 copper to 3/4 pipe.
Test: The boiler was cold started. An aquastat on the boiler return line after the Termovar is set to ON at 155F. This turns on both the boiler and system circulators at the same time. Since the aquastat is fed by gravity flow, when it turns ON, the top of boiler water temperature actually is greater than 155F.
Temperature readings were taken every 10 minutes during an ON or OFF cycle.
Example: At 12:31 the aqustat turned on both circs. This first ON cycle was 76 minutes long before the boiler cycled off. Boiler water input to the HX was 170 and HX return to boiler was 130. The return to boiler after the Termovar was 148, which meant that the Termovar was mixing some boiler output directly back to boiler return. Boiler side BTU's were BOILER INPUT TO HX - BOILER RETURN (deltaT) X 8 gpm x 500 x 0.85. The 0.85 factor relates to 50% antifreeze solution, which has about 85% of the heat capacity of water at 160F.
On the system side, tank input to the HX was 130 and HX output to the tank was 145. System side BTU's were HX OUTPUT TO TANK - TANK INPUT TO HX X 7.5 gpm x 500.
Note: in this first entry BTU's available on the boiler side were 70,400 but that BTU's extracted by the HX were 56,250, for an 80% transfer efficiency. Note also that as system input temperature rises, HX heat transfer efficiency decreases.
Note: that as system input temp rises, the boiler starts to cycle through idle periods. With the given gpm's and HX specs, the system side cannot keep up with boiler output as system temp rises. More gpm's and/or a larger HX would reduce cycling.
Note: if water rather than antifreeze were used in the boiler loop, boiler BTU output to HX would increase by about 18%, and HX output to system also would rise adjusted by the heat transfer efficiency.
Other: the data is what it is. I don't think I made any errors. Obviously, to the extent that temp readings are inaccurate, or gpm's are inaccurate, the BTU calculations will not be accurate.
Have fun for this if it makes any sense to you. Ask questions if you wish.