The answer for me is YES - but I found this info and thought it might make good reading fodder for the masses.......
One of the questions I hear most often from sweeps and fireplace retailers is "When should I insulate a chimney liner?" It's a great question that requires a detailed answer. The most relevant question to many installers regarding insulating chimney liners is "When do I HAVE to insulate one?" This requires looking at the NFPA 211 standard for masonry chimneys and the UL 1777 listing.
NFPA 211 is the code set forth by the National Fire Protection Association for the construction of masonry chimneys. To summarize the code, a masonry chimney is up to the standard when it is built with two critical one-inch air spaces. One between the combustibles outside of the masonry chimney and one between the chimneys masonry structure and the chimneys interior flue tile. Unfortunately, chimneys built up to the NFPA 211 standard are more the exception than the rule.
UL 1777 is the listing which lays out the installation guidelines for stainless steel chimney liner installations intended for solid fuel applications. These are an overwhelming majority of installations performed by chimney sweeps and fireplace retailers and are the installations where, typically, insulation is an issue. The results of the stringent testing process a chimney liner must go through in order to carry the full UL 1777 listing is what determines the specific insulating requirements for each specific chimney liner. During a simulated chimney fire, UL measures the amount of heat transferred from within the liner to the exterior of a non-conforming masonry chimney. If UL measures too much heat transfer, then the liner fails the test. Given the nature of any single wall chimney liner, heat transfer of an uninsulated liner is going to be high. With high density insulation, heat transfer is reduced tremendously. This allows for a safe installation even in a non-conforming chimney, thus allowing a "Zero Clearance" installation.
Any stainless steel chimney liner that carries the full UL 1777 listing can be installed to what is commonly referred to as "Zero Clearance" so long as it is installed in conjunction with its installation instructions. These instructions are laid out by the manufacturer and Underwriters Laboratories or the liners listing agency.
Understanding zero clearance
What specifically does Zero Clearance mean? The Zero Clearance rating refers to the amount of airspace between the chimney liner and the inside of the masonry chimney. It also refers to the airspace between the exterior of a masonry chimney and combustibles. For this reason the listing is sometimes called "Zero - Zero" in the field.
If the chimney liner you are installing carries a full UL 1777 listing to Zero Clearance you can install, within the liner's installation guidelines, with no airspace between it and the inside of the masonry chimney. This also is the case when the chimney has no air space
A liner which carries the full UL 1777 listing can be installed to Zero Clearance within the chimney without insulation so long as the masonry chimney it's installed into meets NFPA 211. Again, if the masonry chimney does not meet the NFPA 211 standard, insulation is required.
What does this mean for the installer in the field? Given that NFPA 211 chimneys are the exception and not the rule, it means you should plan on insulating nearly all of the stainless steel chimney liners you install, if you want them to be up to the UL 1777 standard.
One of the questions I hear most often from sweeps and fireplace retailers is "When should I insulate a chimney liner?" It's a great question that requires a detailed answer. The most relevant question to many installers regarding insulating chimney liners is "When do I HAVE to insulate one?" This requires looking at the NFPA 211 standard for masonry chimneys and the UL 1777 listing.
NFPA 211 is the code set forth by the National Fire Protection Association for the construction of masonry chimneys. To summarize the code, a masonry chimney is up to the standard when it is built with two critical one-inch air spaces. One between the combustibles outside of the masonry chimney and one between the chimneys masonry structure and the chimneys interior flue tile. Unfortunately, chimneys built up to the NFPA 211 standard are more the exception than the rule.
UL 1777 is the listing which lays out the installation guidelines for stainless steel chimney liner installations intended for solid fuel applications. These are an overwhelming majority of installations performed by chimney sweeps and fireplace retailers and are the installations where, typically, insulation is an issue. The results of the stringent testing process a chimney liner must go through in order to carry the full UL 1777 listing is what determines the specific insulating requirements for each specific chimney liner. During a simulated chimney fire, UL measures the amount of heat transferred from within the liner to the exterior of a non-conforming masonry chimney. If UL measures too much heat transfer, then the liner fails the test. Given the nature of any single wall chimney liner, heat transfer of an uninsulated liner is going to be high. With high density insulation, heat transfer is reduced tremendously. This allows for a safe installation even in a non-conforming chimney, thus allowing a "Zero Clearance" installation.
Any stainless steel chimney liner that carries the full UL 1777 listing can be installed to what is commonly referred to as "Zero Clearance" so long as it is installed in conjunction with its installation instructions. These instructions are laid out by the manufacturer and Underwriters Laboratories or the liners listing agency.
Understanding zero clearance
What specifically does Zero Clearance mean? The Zero Clearance rating refers to the amount of airspace between the chimney liner and the inside of the masonry chimney. It also refers to the airspace between the exterior of a masonry chimney and combustibles. For this reason the listing is sometimes called "Zero - Zero" in the field.
If the chimney liner you are installing carries a full UL 1777 listing to Zero Clearance you can install, within the liner's installation guidelines, with no airspace between it and the inside of the masonry chimney. This also is the case when the chimney has no air space
A liner which carries the full UL 1777 listing can be installed to Zero Clearance within the chimney without insulation so long as the masonry chimney it's installed into meets NFPA 211. Again, if the masonry chimney does not meet the NFPA 211 standard, insulation is required.
What does this mean for the installer in the field? Given that NFPA 211 chimneys are the exception and not the rule, it means you should plan on insulating nearly all of the stainless steel chimney liners you install, if you want them to be up to the UL 1777 standard.