Travis Maint. flashing along with Heat Output 4 yellow light? Cause? See Video

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Hope everyone has a wonderful and warm Thanksgiving!
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here
Status
Not open for further replies.

Don2222

Minister of Fire
Hearth Supporter
Feb 1, 2010
9,192
Salem NH
Hello

This video shows the flashing lights on a 7 year old Travis Avalon Arbor Pellet Stove.
See video
To view this content we will need your consent to set third party cookies.
For more detailed information, see our cookies page.


If # 4 Heat output light is flashing:

Owners manual says!
Heater Ran Out of Pellets
• Heater Did Not Start-Up Correctly
• Power Outage
• Restrictor Not Set Properly
• Burnpot Clogged
• Air Leak
• Heavy Ash Build-Up

In this case none of the above is true

Service manual says!
Fault and # 4 (MED) Light Flash = System Snap Disk Fault (pellets run
out & stove goes cold)
Diagnostic Codes (Qualified Service Personnel Only) - Continued
System Snap Disk Fault

Page 4
Fault light and #4 heat indicator blinking.
This fault code is caused by a heat sensitive switch that tells the control
board if the appliance is hot or cold. During operation if the unit runs
out of pellets or looses its fire this switch will communicate to the control
board that the stove is getting cold. The control board will shut off the
auger functions and initiate a twenty minute combustion fan safety cool
down. Another condition that will trigger this fault code is a failed start.
When the appliance is started the control board initiates a 30 minute
timer, if the appliance is cold at the end of this 30 minute start up timer
the control board will indicate a #4 fault and initiate a 20 minute
combustion fan cool down.
Likely cause are:
Unit ran out of pellets.
• Fire went out during operation.
• Unit was cold at the end of a start cycle (fire did not light).
Faulty snap disk. -- Bingo ! ! !

Therefore I replaced the system disc
Also put in 2 new Hi Limit switches

Has anyone seen this failure?

See Pic 1 - White Ceramic System Snap Disc above exhaust blower
 

Attachments

  • [Hearth.com] Travis Maint. flashing along with Heat Output 4 yellow light? Cause? See Video
    SystemSnapDisc.webp
    126.6 KB · Views: 220
Hey Don, as I was reading through and before I got to the bold print (really!!), I was thinking the snap disc ;)
 
Hey Don, as I was reading through and before I got to the bold print (really!!), I was thinking the snap disc ;)
Hi Lake Girl
Yes I thought it was the Low Limit snap disc also, then I did find it in the old 2006 service manual!!! :-)
So I had to pull the stove all apart to replace it but it has been working great for a couple of days now!
 