Hi guys new here am looking at installing econoburn 200 maybe 300 with 2000 gal storage / Has anyone put there tanks underground ? I am considering putting in 2 - 1000 gal propane tanks insulated with foam 3' deep backfilled with sand :coolsmile:
CNY CAT MAN said:Mike ; I am looking at getting 2 used 1000 gal underground propane tanks I will recoat them and install a new anode then spray with closed cell foam probably 4" thick + - R24, I am hoping the ground will also act as an insulator, Looking any and all input
stee6043 said:Me thinks R24 will be SEVERELY inadquate for an in-ground installation. The ground will not act like an insulator, it will act like a heat sink (quite the opposite if insulating). I think R60 would be a bare minimum and even then I think it's light. I have R40 on my indoor tanks and wish I had more.
Everything I have read seems to suggest in-ground is likely one of the least desirable locations for high temperature thermal storage....
CNY CAT MAN said:ewd ; Thanks for getting back with the calcs. I could add more spray foam the foam I would be using is closed cell appiled directly to the tank it should act as mositure barrier as well. I just used it for my run of 1" pex 100' from garage to house , please dont tell me I made a mistake by doing that. PS I'll make sure not to let my sweet thing see your post that sunroom on a cold winter day would sound better to her than a boiler :coolsmile:
You have: (1/24.0 Rvalue) * ((2*((41/2)^2*pi)) + (192*41*pi))in^2 * ((190-40)degF)
You want: btu/hour
1187.9829
You have: (1/30.0 Rvalue) * ((2*((41/2)^2*pi)) + (192*41*pi))in^2 * ((190-40)degF)
You want: btu/hour
950.38632
You have: (1/36.0 Rvalue) * ((2*((41/2)^2*pi)) + (192*41*pi))in^2 * ((190-40)degF)
You want: btu/hour
791.9886
You have: (1/24.0 Rvalue) * ((2*((41/2)^2*pi)) + (192*41*pi) + (2*(41^2)) + (2*192*41))in^2 * ((190-40)degF)
You want: btu/hour
2017.2364
You have: (1/30.0 Rvalue) * ((2*((41/2)^2*pi)) + (192*41*pi) + (2*(41^2)) + (2*192*41))in^2 * ((190-40)degF)
You want: btu/hour
1613.7891
You have: (1/36.0 Rvalue) * ((2*((41/2)^2*pi)) + (192*41*pi) + (2*(41^2)) + (2*192*41))in^2 * ((190-40)degF)
You want: btu/hour
1344.8242
powerspec said:Insect protection! Never would have thought about it. Maybe a concrete missle silo would do. Seriously though direct burial of high density foam is well approved up here and underground bugs are the least of concerns. Check your local codes?
powerspec said:When insulating pipes and round conductors there is point where the added insulation makes more surface area to radiate heat away, called 'critical thickness'. So don't add more than 5 inches of evenly applied high quality foam, that's my take on things.
Press on!
powerspec said:Nofo is correct, critical thicknes refers to the magic value of insulation thickness that best defeats the purpose of the insulation, that of reducing heat loss. The critical thickness for spray foam on these tanks would be very much greater than anyone would afford to pay for. But the same is not true for small diameter pipes. The 5 inch max limit is a practical one as I see it to save money and get the least heat loss for the money spent. I feel that all other forms of insulation are poor compared to the performnce of properly applied high density spray urethane foam. Flat sheets of blue styro are a very poor substitute for underground service on a round hot tank.