Ok, More questions than answers. I have read that any type foil under slab is not effective. It seems that foil needs air space to work properly. Bubble foil bubble is what I installed under 4" slab with 1/2 pex at 1'0" centers.I used 2 inch blue foam (r-10?) on all sides of concrete. Concrete poured 6/08 900 sf. 3 circuits of less than 300 feet.I have read that bubble wrap if you will. is as good as 2" styrofoam. I will direct you to the web page- naturalspacedomes.com radiant floor tests. This seems a little crazy however if the test is accurate and I know of no reason to deny it I would go with bubble wrap. It is easy to install and you can walk on it with out rupturing it like foam. The grade is not as fussy, I chose to overlap about 3" and not tape with duct tape. foil does not go well with concrete (DIRECT CONTACT) but if it is encapsulated (bubble, foil,bubble)it is ok. I believe you want to go for 10x insulating power under the slab.As to concrete think of it this way 3.5: fiberglass insulation is r-11 7.51 FEET thick is r-11. Concrete is a great conductor of heat. This is my 1st post.
RE bubble foil insulation; I don't know of any product in the heating industry , other than Outdoor wood burners, about which so much false propaganda is perpetrated. It falls in the same category as the paint with a supposed R-value of 70 that was on the internet. That company had all sorts of test data to back up their claim also.
The sellers of this product make wild eyed claims of R-values beyond any stretch of common sense and I can show you installation after installation where its use has resulted in extremely disappointing results. A logging company just a couple miles from me put up a 10,000 sq ft repair shop and used the double bubble stuff under the slab and on the edges. They have the largest OWB made by Central boiler and they fire it non stop in order to keep the building above 40*. In mid February there is no snow within 6 feet of the perimeter of that building, which by the way is itself very well insulated.
One of my friends at heatinghelp.com did a real world experiment using different types of insulation under a slab. He had insul-tarp, foam of varying thickness, bubble/foil/bubble, double bubble/foil/double, and a couple other types IIRC. All the slabs were tubed the same and fed the same temp water. The control was an uninsulated slab. After he put heat to them, he took pictures of the slabs with an infrared camera and measured the surface temp. The bubble foil slabs were nearly the same temp as the control (uninsulated) except for a 3" wide band above each tube. The ridgid foam slabs performed best, coming up to temperature far faster and distributing the heat evenly through the width of the slab with far less "striping" being noticed. If you go there and search through the archives you can probably find it. The stuff has been banned in Canada for use not only under slabs but also in buildings IIRC.