Thank you for the thoughtful replies.
I agree with you Yoder, the stove coils need to be below, or at least the outlet of the stove coil needs to be somewhat below the top of the storage tank. The lower, the better. Ideally, the circuit should form a cold trap, with the low point significantly below the bottom of the tank to prevent reverse circulation when the stove is cold. My current setup has the lowest stove coil slightly above the bottom of the tank, and no cold trap for space reasons. Slight reverse circulation does occur, but not enough to present a problem. Since the only source of heat to that tank is the woodstove, there's normally a layer of very cold water that has come into the tank from water use since last firing that seems to inhibit the reverse circulation. If that tank had another source of heat, I think I would have to stop the reverse circulation somehow.
Maple 1, yes, delta T is the biggie that I'm scrapping with at the moment. I'm hoping to get firm data from Kuuma on the output temps at different settings and CFMs, but don't have it at the moment. 500 cfm at 140 degrees seems a reasonable guess to me in the meantime. The math gets fuzzy when I don't really know what the water flow rate is. Flow rate is going to be a function of the amount of heat from the heat exchanger (which gets badly circular), and I think I have to allow for the fact that tube heat exchangers don't like to be run at low flows like the thermosiphon would create. I understand that that they tend to have a laminar flow at low rates where the fluid touching the tube gets hot while the fluid in the center stays colder as it moves through the tube. I'm not a heat transfer engineer, or I'd already have my answers, so I'm not sure how that really affects water with it's great heat transfer ability and stable viscosity, but it's a huge problem with oil, etc. Cooled oil, for instance, forms a thickened layer along the surface of a cooler keeping the hot oil from contacting it. Some turbulence is your friend when transferring heat!
I'm trying to design this thing to thermosiphon, not use a water pump, for a few reasons:
- If I can avoid (cost effectively) another energy input to run the pump, why not do it?
- Less moving parts is always better, if feasible.
- I'm not off-grid, but where I live, the grid is frequently off. A pump is just one more load to provide back-up power for.
- Most importantly - a system designed to thermosiphon is inherently resistant to meltdown should a power or pump failure occur. My backup power is not automatic, and I wouldn't trust it 100% even if it was.
- I'm ashamed to admit it, but I have been trying to save the addition of a circ pump as an ace-in-the-hole. If, after my best efforts to build this right, it doesn't put out quite enough hot water, I can add a pump to hopefully salvage the situation, while keeping the thermosiphon function as meltdown protection.
I'll throw out a bit of detail about what I've been doing with my old setup. It might help you understand where I'm coming from and trying to get to with the new furnace (VF100), but more importantly, it might help somebody with their project or decisions:
Seven or so years ago I bought a home with the smaller model Clayton furnace (#1600 - IIRC) added on to the central propane furnace (which I don't use). I understand that the previous owners had quite some challenges using it. They had the power air inlet on it, and there's three stories plus of straight up metalbestos pipe above the stove. The thing could draft hard enough to empty the ash pan onto the roof! If you lit it, it was pretty much in runaway mode the whole time. It did an excellent job of heating the chimney cap, and not much else, except for some firebox parts that it melted. Ignoring the instructions, I ditched the power inlet blower for a duct control that would shut it down when the power goes out, and added a manual damper in the stovepipe. The Beast, as we call it, was tamed!
I added the 24" firebox DHW coil option from the stove manufacturer, along the side of the firebox, using an 80 gallon electric water heater tank right next to the tank, on a stand as tall as the floor joists would allow. I wanted more hot water, so I added another of these coils, in a custom location, below the top baffle, directly above the fire. This approximately tripled the hot water delivered. It then provided all the hot water my wife and I need to live a normal suburban style life, so I went from using it for tempering, to our normal water heater, with the addition of a temp mixing valve.
Because we have the unusual situation of a heating season that is 46-50 weeks long (we don't usually get measurable snow in August), the Clayton provides all of our DHW for all but 2 weeks to a month of the year.
In winter, I run the fan control to turn on at about 80 degrees, or use a manual always-on blower switch. Even though the DHW tubes are inside the firebox, isolated and insulated from the forced heating air, running the blower significantly reduces the DHW generated. There are two other woodburners in the house I can supplement with, as well, to help keep the house warm, but they have their own issues which I won't go into here.
Conversely, in summer, I bump the fan control up to 200 degrees, and build a small fire periodically out of woodcutting scraps and choke the air down a bit. The stove produces a lot of DHW and little hot air. On a cold summer day, I can use the always-on switch to pull more hot air.
I wondered a lot about the thermosiphon effectiveness before I tried. My results show it works
amazingly well! My cold water from the tank drain goes into the bottom of the bottom loop, exits the top, then is plumbed into the horizontal loop above the fire. Exiting the top loop, it travels over and a couple of feet up, to the port where I removed the top heating element on the tank. The stainless heating coils are 3/4 ID, and the plumbing to them is mostly 3/4 stainless flex, with some 1" fittings at the tank. I have a thermometer probe on the tank a few inches away from this port, and the difference is visible within a couple of minutes of starting a fire. It usually drops a degree or two as the slug of cold water in the pipes is pushed out, then begins to climb.
The last couple of days have been near summer weather, and the wife and I have been away from the house a lot, so it's been showers only, pretty much. With the fan control in the winter setting, I've had to burn 2-3 6x19 lodgepole pine logs per day to keep up with the DHW, and gotten a fair bit of hot air to keep the house from cooling too much. It runs the probe temp from say 114 to 124 in an hour or two. So, yeah, it can really heat water, and knock on wood, I not had a single problem doing it.
Why would I screw with a good thing? Well, to keep this very long story short(er), while it's great for heating water, it's not so good at heating the house. Burning the only wood I have in quantity - lodgepole pine, I have to tend the thing every couple of hours. The more wood I put in it, the more heat I get, but the efficiency gets even worse, and the stove actually needs reloaded more often. A cold house in the morning is a given. I'm about to freak some of you completely out, but my target daytime temp in the house is 54-60 depending on the weather, so a cold morning house temp can be 50 down to I've seen 36 on the bedroom thermometer. 50 is ok with me, if I could give it a quick bump when I'm ready to get up, but the Clayton will neither keep burning for more than 3 hours after I go to sleep, nor does it have the horsepower to warm things up with any speed when I get up. So, I'm hoping to improve both of those with the new Kuuma. And I wouldn't mind only feeding it every 4-6 hours during the day, either.
I hope someone finds something useful in my experience, and I'm still hoping to benefit from other's experiences with finned heat exchangers and water heating. Thanks everybody!