i removed the little black jumper. I don’t have a thermostat yet. I was just jumping the two connectors on the board together, just to test things out.. although I never did it very long? Wonder if it takes a minute for the board to recognize the call for heat?
 
Wonder if it takes a minute for the board to recognize the call for heat?
Around 5 minutes to see any difference in flame height and more like 15 - 20 minutes for stove to reach max temperature for the set heat range. Does you stove go from 1-5 or 1-9 heat range. With the jumper removed , If 1-5 set it on 4 if 1-9 set it on 5-7 if the flame burns only at a idle the thermostat circuit is working. Look for the blinking dash between heat range letter and number means stove is ramping.
 
Mine goes 1-5. The stove doesn’t seem to recognize the jumper being removed. When I remove the jumper and don’t have anything hooked to the thermostat leads it still acts like the jumper is still there because when I adjust the heat setting up to anything over 1 it will stay on that setting and not return to 1.. also think I have an auger problem, when I turn it up the auger seems to run more but there are a lot of runs where little to no pellets come out. So I guess I’ll be pulling it back out
 
Auger sounds right, sometimes a lot drops some times a little if you watch long enough you might even see it drop nothing. It depends a lot on length of pellets 1/4 inch pellets drop more often the 1 inch pellet.

Does the dash blink when the jumper is not in place?

[Hearth.com] Ussc 6041i
 
Setting won't change but the dash blinks as in the above GIF.
Should also check feed rates using C codes. C2 and C3 2 should be 2.00 and 3 5.00. Never no previous owner could have changed them

ADJUSTING OPERATIONAL CONSTANTS
TO ADJUST THE OPERATION CONSTANTS, PRESS & HOLD THE “MODE” AND “AUGER DELAY”
BUTTONS SIMUTANEOUSLY FOR 3 SECONDS. THE DISPLAY WILL SHOW “C-1”. USE THE HEAT
RANGE UP OR HEAT RANGE DOWN BUTTONS TO CHANGE THE CONSTANT NUMBER (SEE THE
LIST OF VALUES BELOW). WHEN THE DESIRED CONSTANT IS DISPLAYED, PRESS THE “ON”
BUTTON UP, TOGGLING BETWEEN VIEWING AND EDITING THE VALUE. WHILE EDITING A
PARAMETER, USE THE “AUX UP” AND THE “AUX DOWN” BUTTONS TO ADJUST THE VALUE TO
THE DESIRED POINT. THEN PRESS “ON” AGAIN TO RETURN TO THE CONSTANT NUMBER LIST.
PRESS THE “OFF’ BUTTON TO EXIT THE ADJUST OPERATIONAL CONSTANTS MODE.
 C-1- RESET TO DEFAULTS (HOLD “MODE” AND “AUGER DELAY” BUTTONS FOR 3 SECONDS
TO RESET ALL TO DEFAULTS.
 C-2- FUEL LBS. PER HOUR HR-1 (0.01-6.50) - THIS IS THE FUEL RATE IN POUNDS PER
HOUR FOR A HEAT RATE SETTING OF 1 The DEFAULT IS 2.00 LBS..
 C-3- FUEL LBS. PER HOUR HR-5 (0.01-6.50) - THIS IS THE FUEL RATE IN POUNDS PER
HOUR FOR A HEAT RANGE SETTING OF 5. THE DEFAULT IS 5.00 LBS. THE FUEL RATES
USED BETWEEN SETTINGS 1 AND 3 ARE LINEARLY INTERPOLATED BETWEEN THE TWO
SETTINGS.
 

Attachments

Ok that makes sense now.. I thought that when there was a no heat call it would show hr-1 and when there was a heat call it would show hr-4( or whatever it was set to). But it just flashes on whatever hr- you have it set two for the heat call even though it’s just running on hr-1. I’ll test again tonight
 
I thought that when there was a no heat call it would show hr-1 and when there was a heat call it would show hr-4( or whatever it was set to). But it just flashes on whatever hr- you have it set two for the heat call even though it’s just running on hr-1. I’ll test again tonight
correct just flashing dash shows something is happenings and flame size
 