Venting a pellet stove

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Hope everyone has a wonderful and warm Thanksgiving!
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here
Status
Not open for further replies.

MacKay

Member
Hearth Supporter
Jan 21, 2008
62
SW. Pennsylvania
I have a venting question. I would like to install a pellet stove in a soon to be finished basement. The basement is completely below grade. I was looking into the Harman XXV because I could vent from the top then out through the wall. The main question I have is how high do I have to run the pipe above grade. And as a follow up, there is a window on the first floor right above that location, is it a problem?
Derek
 
Check the Harman online manual. most of them cannot vent under a window it has to vent above or away. Also have to check bilding codes

Shawn
 
They make snorkel kits, for that type of install. Minimum 18" above grade. You need to be a minimum 48" away from doors or windows.
 
If I am required to be 48" away from windows and door, I won't be putting a decorative pellet stove in my basement. I don't have a spot where I have that clearance. I could potentially put in an add-on furnace if I were allowed to also vent into the chimney for the furnace.
 
Well if you have those small type basement windows, you can actually vent straight out through that window. obviously blcoking it off. Also, you can not by code put more than one appliance in a flue.
 
Basement windows are not a problem. It would be the first floor windows that would interfere. What is the danger of venting two appliances through the same chimney?
 
You should be able to get the owners manual, with venting instructions, online in a PDF format. You might also want to check out the instructions on Simpson's website. Your install sounds doable but it is a little more complicated than normal. I see you're in PA so you'll need to get the end of the vent above your normal snow line as well. It's likely that you'll need to run the pipe laterally, at an angle, once it exits the wall to achieve the clearance you need from the window before going vertical.
 
DMM said:
Basement windows are not a problem. It would be the first floor windows that would interfere. What is the danger of venting two appliances through the same chimney?

Backdrafting. No solid fuel appliances can share a flue, ever.
 
DMM said:
If I am required to be 48" away from windows and door, I won't be putting a decorative pellet stove in my basement. I don't have a spot where I have that clearance. I could potentially put in an add-on furnace if I were allowed to also vent into the chimney for the furnace.

You could go through the wall/window and then up the wall and vent above the roofline.
 
• Follow NFPA 211 rules listed below for venting system termination location relative to windows and other openings in the dwelling.

o NFPA 211 (2003 ed.) Section 10.4 Termination: 10.4.5
(1) The exit terminal of a mechanical draft system other than direct vent appliances (sealed combustion system appliances) shall be located in accordance with the following:

(a) Not less than 3 ft. (.91 m) above any forced air inlet located within 10 ft. (3.0m).

(b) Not less than 4 ft. (1.2 m) below, 4 ft. (1.2 m) horizontally from or 1 ft. (305 mm) above any door, window or gravity air inlet into any building.

(c) Not less than 2 ft. (0.61 m) from an adjacent building and not less than 7 ft. (2.1 m) above grade when located adjacent to public walkways.

• Distance between the termination opening and grade should be a minimum of 24 in. contingent on the grade surface below the termination. When determining the termination height above grade, consider snow drift lines and combustibles such as grass or leaf accumulation. In areas where significant snowfall is possible, the termination height must be sufficiently high to keep the termination free of snow accumulation.
 