geka said:
The home is 3 years old...very well insulated we hope. There is radiant heat in the first floor but it takes forever to heat up. Cathedral ceiling in part of this. 2000 square feet is a good estimate of what would be heated . Would love to do ventless. This stove would basically just be used in emergency situations and to warm the place up till the radiant is up and running well and who knows it may be used in the cooler weather to take the chill off instead of turning the main heat on. Appreciate your input. Thanks.
Well for that area to get heated, I'd say you'd need 30 BTU/SF - so 60K BTU OUTPUT...
At 75% efficiency, you'd need 80K INPUT
You're getting into a small furnace range there..
We sell a couple of DV units that are in the 40K INPUT range & at 75% efficient will OUTPUT 30K,
or about 1/2 of what you need...
As far as the vent-free units, we don't offer em, recommend em or service em...
They ARE 99% efficient, but for every 100K BTU, they'll add a gallon of water vapor into your home,
(which in your newly-built, well-insulated home is DEFINITELY not good)
along with (what the manufacturer considers an "acceptable amount" of) carbon monoxide...
Yeah, yeah, yeah... they have "Oxygen Depletion Sensors (ODS) which are designed to shut the units down
when the CO gets a little too much for safety...
Do you want to trust your life to a $150 pilot assembly?
There ARE odors associated with these products that you or I may not notice,
but some people with respiratory ailments will...
Bottom line?
It's your house & your life...
You won't find a whole lot of people who recommend them...
As far as the "my gas cook stove is vent-free" argument...
Lots of folks DIE when they try to heat their homes with gas cook stoves...
Anyhoo, you probably won't be able to heat your ENTIRE residence with ONE gas stove,
but you should be able to make part of it comfortable...