Water to Air HX btu output vs input water temp

3fordasho Posted By 3fordasho, Jan 4, 2018 at 9:19 AM

  1. 3fordasho

    3fordasho
    Minister of Fire 2.
    NULL
    

    Jul 20, 2007
    741
    150
    Loc:
    South Central Minnesota
    I'm starting to realize that heating 3 separate structures with 4 different wood burning appliances is not sustainable long term ;-).

    One of the structures is suitable for boiler with storage and lots of wood storage. First thought is a Garn JR because of simplicity and I am with in 100miles of their manufacturing facility.

    So of the three structures needing heat, the house being the main concern is currently set up with 120kbtu propane FA, Tundra wood furnace tied in parallel, and a Progress Hybrid on the main level. The Tundra would go away, Progress Hybrid would remain for when I want to look at a fire.

    Now to my question - plenum in the FA furnace is large, can probably fit a 22x25 or somewhat larger HX. Trying to determine how low I can go on storage temps and get any meaning full output. Output ratings I've found so far are all at 180F input temp, ~21 gpm , and CFM air flow. Looking for a calculator, output vs input temp chart, or even what others have experienced.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  2. stee6043

    stee6043
    Minister of Fire 2.
    NULL
    

    Aug 22, 2008
    2,590
    246
    Loc:
    West Michigan
    I found the lowest useable temp to be 140 with my "off the shelf" water-to-air heat exchanger. If I were to do it again I'd have a custom coil built for the plenum rather than just buying one that fits dimensionally. With a proper coil you can go lower with your input temps and still get reasonable fan run times. At 140 my furnace fan was running for a noticeably longer time per cycle. Not desirable...
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  3. dogwood

    dogwood
    Minister of Fire 2.
    NULL
    

    Mar 22, 2009
    801
    39
    Loc:
    Western VA
    After reading Pybyr's posts on the subject a few years back, I ordered mine through Nationwide Coils, www.nationwidecoils.com/ . I spoke to someone named Ross if I remember. They will custom design a water to air hx to meet your specifications, give you a quote and send you a submittal sheet with more info on it than anyone could possibly understand. Mine was designed to work to work with temps down to 140F. You have to know what the air flow of your furnace is when you call.Their phone number is 888-549 9616. My oversized w/a hx from them has worked as designed three years running now. If I had to do it over I would have had specified larger fittings to connect to my piping.

    Mike.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  4. tom in maine

    tom in maine
    Minister of Fire 2.
    NULL
    

    Apr 4, 2008
    914
    134
    Loc:
    Searsport, Maine
    I am associated with another company that has air to water heat pumps. We also offer water to air fan convectors that are a great heat distribution device that can operate down to 90F doe space heating.
    I am usually using one at 120F. There are three sizes and they are very quiet.
    They are on www.heatingstuffllc.com
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    Highbeam likes this.
  5. jebatty

    jebatty
    Minister of Fire 2.
    NULL
    

    Jan 1, 2008
    5,594
    830
    Loc:
    Northern MN
    If you need supply water much hotter than 140F, I suggest you talk to Garn as how the Jr would work to meet your needs.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  6. Woodfarmer1

    Woodfarmer1
    Member 2.
    NULL
    

    Nov 10, 2013
    226
    27
    Loc:
    Bowmanville, On,Can
    It is my experience that the Garn jr will not deliver. I can get just over 160* to my secondary but that temp is not sustained for more than a couple hours. It likes to sit at 140*.

    If it was installed right beside the furnace those times may improve.

    I fired the boiler last night at 11 (after Canada won Gold at the World juniors) so by 1am the Garn temp would be say 190* +. For my radiant heat it would be around 160* + usable.
    This morning at 8am, the Garn was at 146* and the usable at the secondary was 124*.
    I have rads and in floor.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  7. jwise87

    jwise87
    New Member 2.
    NULL
    

    Dec 21, 2017
    19
    6
    Loc:
    Southern Illinois
    Depends on what you are used to on the usable temp. We had a heat pump in our house that put out luke warm air at best, so I put the kick out temp all the way down at like 80* for when it would use the heat pump and when it would use the boiler, and it felt like the heat pump. However I usually ran my temps somewhere between 155* and 175* depending on temp. I was heating a 2400 sq/ft newer built house and had about 225 gallons of storage and if I let my fire went out in the night it would drop maybe 50-75* by morning. As far as storage goes on wood boilers the more you have the harder it is to recover after a mistake like letting the fire go out.
     
  8. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    8,408
    1,578
    Loc:
    Nova Scotia
    Not sure about the wording on that one. I don't think there is any disadvantage to more storage, recovery wise, as long as things are plumbed right. Even if my storage is stone cold, I can have 160 water going to the house 20 minutes after lighting a fire. So it recovers quick and size of storage doesn't matter. It takes longer to recharge bigger storage, yes, but if you put the same amount of heat into bigger & smaller storage, they should put out the same amount, again, as long as plumbed right (stratification is key). You have to burn longer to fully charge bigger storage, yes, of course, but it will heat your house for a correspondingly longer time, after the fire is out.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  9. rkusek

    rkusek
    Minister of Fire 2.
    NULL
    

    Mar 19, 2008
    589
    35
    Loc:
    Nebraska
    It depends if you are used to lukewarm heat pump output temps or much warmer gas forced air heat register temps. My off the shelf WA/HX was able to maintain the 68 setting we had using only 100-120 degree water this past week with below zero temps. My load bridged on the -19 night and woke up to 64 degree house. Definitely cannot bring it up to temp with 100-110 degree water though. Kicked on emergency backup 15kw heat on the furnace for an hour and only gained a degree. Output was not much warmer than wood HX output either. I think the custom HX would be worth the money. You still have the LP option to cover the rare catch up situations. The Garn is something I wish I had done for simplicity reasons but I don't mind the blower fan running more. Some people might though.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  10. rkusek

    rkusek
    Minister of Fire 2.
    NULL
    

    Mar 19, 2008
    589
    35
    Loc:
    Nebraska
    3 structures? Wouldn't the 1500 be better than the Jr?
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  11. rkusek

    rkusek
    Minister of Fire 2.
    NULL
    

    Mar 19, 2008
    589
    35
    Loc:
    Nebraska
    Eko 40 with 40 degree 30x60x14 pole barn and 64 degree house wouldn't go above 159 for the entire burn on that cold morning. Most winter days it works just fine though.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  12. 3fordasho

    3fordasho
    Minister of Fire 2.
    NULL
    

    Jul 20, 2007
    741
    150
    Loc:
    South Central Minnesota
    Perhaps. Besides the house, one of the structures is where the boiler will be located (24x48' insulated) and keeping it above freezing will be acceptable, then there is a smallish insulated office/well equipment room in the 60x104' pole barn that I keep at 40F. So two of the three structures have pretty small heating loads. House is 3400 sqft and well insulated and sealed for a 1982 build.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  13. jwise87

    jwise87
    New Member 2.
    NULL
    

    Dec 21, 2017
    19
    6
    Loc:
    Southern Illinois
    I was not thinking of added storage when I said that, I had the volume of the water in the water jacket in mind. It would take me a hours to get my water up to temp in my old stove. I pulled water from near the bottom and returned it to the top so I would have constant circulation in water jacket, but that meant I was in trouble if my temps dropped.
     
  14. 3fordasho

    3fordasho
    Minister of Fire 2.
    NULL
    

    Jul 20, 2007
    741
    150
    Loc:
    South Central Minnesota
    Seem to be reading here that the Garn shines best with low temp emitters like radiant floor. Not an easy thing to retrofit into existing structures.
    Garn rates their boilers storage from 195f-120f. Would be nice to get some usable heat down to 120f but don't know if that is possible in a water to air HX. Should I be looking at different boiler designs? Not locked into a Garn by any means.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
    laynes69 likes this.
  15. gfirkus

    gfirkus
    Member 2.
    NULL
    

    Nov 28, 2014
    43
    18
    Loc:
    central wisconsin
    I’ve had water temp down to 120 and it still blew enough heat. Get the largest hx that fits your plenum . Make sure the supply goes to top of hx. I only have 1500 sf ranch house tho. Check out the Switzer boiler. I had about $750 into going to get it. Overall it was cheaper than the garn and is pressurized. Treat the water once and your done.
     
  16. 3fordasho

    3fordasho
    Minister of Fire 2.
    NULL
    

    Jul 20, 2007
    741
    150
    Loc:
    South Central Minnesota

    Thanks for that link - they provided a quote and specs with in minutes of submittal. If I'm reading the submittal data correctly I should still see 60k btu output at 120F water temps.
     

    Attached Files:

    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  17. 3fordasho

    3fordasho
    Minister of Fire 2.
    NULL
    

    Jul 20, 2007
    741
    150
    Loc:
    South Central Minnesota
    Thanks for the reminder about Switzer, they will definitely be considered. Especially after reading that thread back in 2011 about the corrosion issue in the Garn, though seems to be possible in closed systems as well.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  18. surefire

    surefire
    Member 2.
    NULL
    

    Nov 15, 2014
    45
    2
    Loc:
    Saskatchewan
    I think that corrosion issue was due to improper operations ie boiling and lack of a water test before summer layup, IIRC.
     
  19. surefire

    surefire
    Member 2.
    NULL
    

    Nov 15, 2014
    45
    2
    Loc:
    Saskatchewan
    What were your specific details provided to Nationwide Coils? I might be missing something, but doesn't the SCFM seem really high on the submittal?
     
  20. 3fordasho

    3fordasho
    Minister of Fire 2.
    NULL
    

    Jul 20, 2007
    741
    150
    Loc:
    South Central Minnesota

    Info I gave them but need to verify further. Thanks for pointing out that parameter maybe off.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  21. dogwood

    dogwood
    Minister of Fire 2.
    NULL
    

    Mar 22, 2009
    801
    39
    Loc:
    Western VA
    Your welcome. That's the same format submittal sheet they sent me years back. The Air Flow (SCMI) listed on my sheet is 1320 and I've a fairly big furnace. Check your furnace's manual to be sure. Some have multiple air flows and settings.

    When the original furnace died a furnace service person had to do some adjustments to the new furnace to get the airflow matched to the w/a heat exchanger's design parameters. Nothings ever easy. Good luck

    Mike
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  22. surefire

    surefire
    Member 2.
    NULL
    

    Nov 15, 2014
    45
    2
    Loc:
    Saskatchewan
    Tim, was there any follow up on that parameter?
     
  23. 3fordasho

    3fordasho
    Minister of Fire 2.
    NULL
    

    Jul 20, 2007
    741
    150
    Loc:
    South Central Minnesota
    I am going to have them recalculate with 1400 cfm air flow (after reviewing the furnace specs this seems more realistic)
    I can also go larger HX if I move it up higher in the plenum but will have to go from 6" coil thickness to more like 4". Wish I had their sizing program so I could play with all these parameters myself.
     
    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  24. 3fordasho

    3fordasho
    Minister of Fire 2.
    NULL
    

    Jul 20, 2007
    741
    150
    Loc:
    South Central Minnesota
    New coil specs @ 1400 cfm. Changed coil size to 26 x 26"x 4". 55kbtu delivered @120F. Should still heat the house at 120F supply temp.
     

    Attached Files:

    Stop hovering to collapse... Click to collapse... Hover to expand... Click to expand...
  25. surefire

    surefire
    Member 2.
    NULL
    

    Nov 15, 2014
    45
    2
    Loc:
    Saskatchewan
    Nice. You're okay with a decreased output of 6.3kbtu? Maybe not a big deal.
     