I am ready to start cutting pipes and put together the near boiler plumbing loop for an EKO 60, with a 500 gal LP storage tank. I can't figure how to draw a decent picture and post it, but the fundamentals are pretty simple. The supply comes out of the top of the EKO 60 in 2" - but I will be reducing it to 1.5" black iron. The primary loop is the "normal" configuration, going to the tank in the top, and out the bottom for the return. There will be a pipe connecting the supply to the return, with a balancing valve, to a Danfoss 3-way thermostatic valve, controlling the return water temp. So this primary piping would look like two adjacent rectangles, the supply on top, the return on the bottom, with the balancing valve/piping being the shared vertical line.
Every book I have read, including the I=B=R guide, Holohan's book(s) and Siegenthaler all strongly recommend the combination of the placing the expansion tank (the Point of No Pressure Change), and the supply and air scoop, before the circulator, on the supply side out of the boiler. I understand their reasoning, and it makes sense. Based on that, it seems the worst thing to do would be to place the circ pump on the return side, and the expansion tank/supply/air scoop on the supply side, separated from one another. Yet, most of the diagrams I have seen, as well as the one supplied by the vendor who sold me the EKO, recommends placing the primary circ on the bottom, return run, and the expansion tank/air scoop on the top, just out of the boiler supply (along with the low water cutoff, venting valve and pressure relief valve).
So, if I plumb it "by the book", I would place the primary circ high up on the upper supply line run, after the expansion tank combo. If I follow the other advice, I would place it on the bottom return piping. One reasoning I have heard for placing it on the bottom return piping is that is will be the last thing in the system to run out of water if there is a leak - but the low water cutoff should have stopped everything long before that.
Should I go ahead and do it by the book, which means placing the primary circ on the upper piping run, after the expansion tank, or go ahead and put it on the bottom return run?
The head pressure on this 1.5" primary loop is very low - 4 feet of head or less, and the return line is 37" or so below the top of the water level in the 500 gal storage tank, so the suction side of the circ has little danger of seeing any starvation.
I know this has been discussed in previous threads, but I am still at a bit of a loss as to why it would be "wrong" to put the circ on the top supply side, as all the books recommend? Is there something different about having a storage tank, that changes the reasoning here?
Every book I have read, including the I=B=R guide, Holohan's book(s) and Siegenthaler all strongly recommend the combination of the placing the expansion tank (the Point of No Pressure Change), and the supply and air scoop, before the circulator, on the supply side out of the boiler. I understand their reasoning, and it makes sense. Based on that, it seems the worst thing to do would be to place the circ pump on the return side, and the expansion tank/supply/air scoop on the supply side, separated from one another. Yet, most of the diagrams I have seen, as well as the one supplied by the vendor who sold me the EKO, recommends placing the primary circ on the bottom, return run, and the expansion tank/air scoop on the top, just out of the boiler supply (along with the low water cutoff, venting valve and pressure relief valve).
So, if I plumb it "by the book", I would place the primary circ high up on the upper supply line run, after the expansion tank combo. If I follow the other advice, I would place it on the bottom return piping. One reasoning I have heard for placing it on the bottom return piping is that is will be the last thing in the system to run out of water if there is a leak - but the low water cutoff should have stopped everything long before that.
Should I go ahead and do it by the book, which means placing the primary circ on the upper piping run, after the expansion tank, or go ahead and put it on the bottom return run?
The head pressure on this 1.5" primary loop is very low - 4 feet of head or less, and the return line is 37" or so below the top of the water level in the 500 gal storage tank, so the suction side of the circ has little danger of seeing any starvation.
I know this has been discussed in previous threads, but I am still at a bit of a loss as to why it would be "wrong" to put the circ on the top supply side, as all the books recommend? Is there something different about having a storage tank, that changes the reasoning here?