This is the point I was trying to make in this thread:
https://www.hearth.com/talk/threads/45102/ in post #21
So what are the facts:
1. boiler is most efficient with inlet at 140 degrees and high flow?
2.keep boiler from idling if possible.
3. pressurized storage is best charged with high temp water, keeping strong thermocline between the charging water and the cooler water in the rest of the tank.
I have witnessed this in my DHW tank, with cold well water in the tank and hot water on top you can follow the temp gradient down the tank as it charges, It
hardly mixes at all.
4. as long as storage is as low/lower than 140 you can always mix with warmer outlet water to maintain 140 at the boiler inlet.
Now this is the easy part... Good control logic can accomplish most this with no problem. I think that it would be better to sacrifice some efficiency at the boiler
to only run the water through once to charge the tank. IE maintain 180-185-190 whatever outlet temp and run the tank full through ONE time.
So what are the thoughts on keeping the tank from mixing during the discharge phase? My system returns water ~15 degrees lower than the feed temp so
do i slow down the flow or try some fancy scheme of returning the water to different levels of the tank? I think the answer is slow the flow but then how much
can I get away with and still heat the house. This is what is screwing me up right now, no matter what I do charging it gets mixed during discharge and fouls up
the works.
I think I need to put in an order for that fancy variable speed unit you have Nofo.Hmmmmmmmmmm.
I want to try pressurized storage so bad y'all have no idea. My wife is going to flip. I call it a hobby, She will tell you it's a sickness.
Kris