I'm trying to help a friend who just bought an EV and wants to install a 48 amp charger (EVSE) for it. He's installed 120vac circuits before, but I think this is a little over his head. He wants to mount it on the edge of a deck, at a location that is about 15ft distant from a corner of the house where the main load center is located in an interior wall; thus some of the wire will be in a wet location.

The main problem is that an EVSE is considered a continuous load, and therefore the circuit must be up-sized by 25%, so a 60 amp circuit is required. Some people are under the misapprehension that 6awg NM-B (Romex) can be used for a 60 amp circuit, but this is false - see the attached ampacity table and recall that the 60-degreeC column must be used for NM-B (and UF-B). It can be used for 55 amp circuits, and the "step up" rule allows 60 amp breakers to be used on 55 amp circuits. Hence the confusion. So something else is needed.

One option is to run THWN in conduit. The problem with this is that it'd be pretty tough to run conduit up to the panel. Perhaps we could run 4awg Romex down to a junction box, and then transition to conduit with 6awg THWN. Another option would be to use armored cable (type MC), but it'd need to be the type that is sheathed in a PVC jacket (for water-resistance). This is called Teck90 cable: https://nassaunationalcable.com/pro...QRzm70dpv9KqQps6H-JOK1bJEItgghQBoC1OIQAvD_BwE

It's pretty damn expensive, and it requires special terminations (at least at the end that's exposed to weather) and those appear even more expensive.

I suppose we could just use 4awg UF-B, except I'm not sure that even exists, and it'd be a PITA to work with if it did.

So I'm wondering if there's something else I'm not thinking of.

My inclination is to tell him to exchange the 48 amp EVSE for a 40 amp one, and just use 6awg UF-B the whole way. My household has not one, but two, EVs and we are perfectly content with a 40 amp EVSE.
 

Attachments

Last edited:
My inclination is to tell him to exchange the 48 amp EVSE for a 40 amp one, and just use 6awg UF-B the whole way. My household has not one, but two, EVs and we are perfectly content with a 40 amp EVSE.
So the Tesla wall charger allows you to set the circuit ampacity when it’s commissioned. Tell him to look at the manual and see if that it possible. I’m quite happy with my 16A charging rate. It will be easier to add a second 20A to charge a second EV and upgrade the 20A to a 40A or manage share circuit charging.
 
Ok, just found out they DID buy the Emporia charger. So I'm gonna recommend running it at 40 amps. So we can either (1) go 6awg UF-B the whole way, or (2) come down from the panel with 6awg NM-B, and then PVC conduit with 8awg THWN to the charger.

I hate working with UF-B, but option 2 requires a junction-box, and then probably some liquid-tight for the last couple feet into the EVSE, so probably quite a bit more expense for materials.

Assuming it's ok to run UF-B un-protected along the bottom of the deck. Also might need to briefly transition to conduit to get a water-tight entrance into the bottom of the EVSE, and to protect it coming up the side of the deck.
 
Last edited:
  • Like
Reactions: EbS-P
There's much controversy over whether it's ok to use 6awg NM-B for a 48 amp EVSE. I asked my AHJ and he said no, but said if I know of any exceptions to please tell him. (He's that rare bird willing to discuss and admit he might be wrong). This thread mentions some exceptions, none relevant to me: https://forums.mikeholt.com/threads...-charging-station.2591385/page-2#post-3055762

But the beauty of that Emporia unit is that you can dial it in. I can set it to 44 amps and just meet the 55 amp spec. Or if, in the future, someone decides 48 amps really is ok, I can change it to that. But I don't really care: we have two EVs an are content with 40.
 
There's much controversy over whether it's ok to use 6awg NM-B for a 48 amp EVSE. I asked my AHJ and he said no, but said if I know of any exceptions to please tell him. (He's that rare bird willing to discuss and admit he might be wrong). This thread mentions some exceptions, none relevant to me: https://forums.mikeholt.com/threads...-charging-station.2591385/page-2#post-3055762

But the beauty of that Emporia unit is that you can dial it in. I can set it to 44 amps and just meet the 55 amp spec. Or if, in the future, someone decides 48 amps really is ok, I can change it to that. But I don't really care: we have two EVs an are content with 40.
Model 3 RWD is limited to 32 amps. What happened to teslas 80 amp charger. That’s right not available anymore. Anything over 40 amps is overkill unless you come home every night and need a full charge. And I’m sorry you’re spending that much time in thr car.
 
Might be an overly simple question, but can the charger be mounted in a different spot so that the wire isn’t an issue?
 
Might be an overly simple question, but can the charger be mounted in a different spot so that the wire isn’t an issue?
I don't think so. But how could the wire not be an issue ?
 
I have the emporia charger. I ran 4awg aluminum SE cable on a 60A breaker to a 60A disconnect box. Hooked the whip from the evse to the disconnect. Easy peasy.

ETA: in case the benefits weren't self evident.
SE cable can be run exposed outdoors. Aluminum because... why copper? And the disconnect was $12 whereas an similar sized "junction box" is north of $30 and doesn't include lugs.
 
Last edited:
mount it on the house. No need to route the wire through the deck underside.
Not close enough to parking area (yes, I know the cord is typically 25ft long).
 
Model 3 RWD is limited to 32 amps. What happened to teslas 80 amp charger. That’s right not available anymore. Anything over 40 amps is overkill unless you come home every night and need a full charge. And I’m sorry you’re spending that much time in thr car.
I thought our old ClipperCreek L25 would need replacement for the EV6's big battery but we've gone 2 yrs. with it L2 charging at 20a and it's been fine for our lifestyle. If one regularly had a long drive starting at 5am after arriving home at 11pm, then that would warrant a higher rate of charge. That's Uber driver level. However, if one is home at 6pm and heads out for a 30-40 mile drive to work at 7am, then no problem at all getting a good charge up to say 80%, even at this lower rate of charge.
 
  • Like
Reactions: EbS-P
I thought our old ClipperCreek L25 would need replacement for the EV6's big battery but we've gone 2 yrs. with it L2 charging at 20a and it's been fine for our lifestyle. If one regularly had a long drive starting at 5am after arriving home at 11pm, then that would warrant a higher rate of charge. That's Uber driver level. However, if one is home at 6pm and heads out for a 30-40 mile drive to work at 7am, then no problem at all getting a good charge up to say 80%, even at this lower rate of charge.
That use case probably covers 70-80% of drivers.
 
That use case probably covers 70-80% of drivers.
Yes, it's fine for most scenarios and gentler on the car's inverter and battery too. A higher amperage connection would be necessary if the car is set up for V2G or V2H, if the car and charger support it.
 
look at your type of wire, it might prove to be cheaper
 
the faster you charge takes life off the battery. you can get tesla charges at 100 amp but the salesman if he is worth his weight in gold will tell you the same thing
 
you can get tesla charges at 100 amp but the salesman if he is worth his weight in gold will tell you the same thing
Most aren't even worth their weight in lead!
But apparently even lead is worth more than it used to be...bought a regular ole car battery lately?! !!!
 
the faster you charge takes life off the battery
I know that's true for fast charging (Level 3) versus Level 2. But is it really that significant for the various amperages of Level 2 that we're discussing here ?
 
I know that's true for fast charging (Level 3) versus Level 2. But is it really that significant for the various amperages of Level 2 that we're discussing here ?
No it’s not. The data I have seen on Teslas showed very little degradation difference between fast charging and level 2. From my understanding the worst thing for a battery is storage at high temps and high state of charge. Think 90+% over 90 degrees. Oven if charging to 100% it’s not over 90% very long.

Time will age a decent battery faster than DC Fast charging. I charges for a year and a half and saw less than 8 miles of degradation on an 8 year old battery.
 
Age, but most importantly - battery chemistry and the charging system in the car. This recent study is interesting. Unfortunately, it's Euro-centric so the Mach-e, GM ultium batteries, etc. are not included, at least not in the top 20.

Earlier battery tech appears to have faired worse but even the last of the top 20 wasn't too bad at 91% capacity after 62,000 miles.

 
  • Like
Reactions: EbS-P
My Tesla has 66kbmiles and is 9.5 years old. I’m like 83% percent of as original range but what is that really. It probably has like 5% or more reserve power and it’s all a software number anyway.
 
I think were going to stick with the EV6 for a while longer.
 
  • Like
Reactions: EbS-P
I think we’re going to stick with the EV6 for a while longer.
Once an EV is owned outright it makes financial sense to keep them on the road even if they need maintenance. Until the battery dies. If The Tesla died tomorrow my fuel bill would be 3k a year to drive the van. Diesel prices are over $5 a gallon here.
 
And batteries keep getting cheaper and better every year.
 
  • Like
Reactions: EbS-P
Once an EV is owned outright it makes financial sense to keep them on the road even if they need maintenance. Until the battery dies. If The Tesla died tomorrow my fuel bill would be 3k a year to drive the van. Diesel prices are over $5 a gallon here.
I hear you. Gas is north of $6 locally and diesel pushing $7.