Flue Liner - company says it can't install - are they right?

Post in 'The Hearth Room - Wood Stoves and Fireplaces' started by RoderickSteiner, Jan 25, 2013.

  1. RoderickSteiner

    RoderickSteiner New Member

    Joined:
    Jan 25, 2013
    Messages:
    7
    Hello,

    I'm so glad I found this forum.

    I had completed the purchase of an Osburn 1600 wood stove (with a refundable deposit) to put in my basement in Quebec. I live in the basement and rent the upstairs, which has a wood stove insert using a separate flue. The installers came and looked at the flue. They were planning to insert a 6 inch flue because many tiles are cracked or broken. But they told me that it would be impossible because the opening was too small.

    They also informed me that they do not install 5" flues because they have far too many problems with the stoves smoking.

    Their only recommendation was that I seek out a mason. I have spoken to a mason. He is going to have a look but because it's an interior flue, it seems he won't be able to do anything to help.

    Anyways I'm on a tight budget (just bought my first house), and I couldn't afford to pay thousands for a mason on top of the current costs.

    Is it true that a 5" won't work? Could the tiles be removed to make room for the 6"? Am I just plain screwed?

    Thanks for reading.

    Helpful Sponsor Ads!





  2. pen

    pen There are some who call me...mod. Staff Member

    Joined:
    Aug 2, 2007
    Messages:
    7,020
    Loc:
    N.E. Penna
    If it's a tall run, 5.5 can work. However, the manual of most stoves states not to use a liner that is smaller than the stove collar outlet. So, even if you used a 5 inch, it may not be compliant with the stove company's minimum requirements for the installation.

    When it comes to the mason, it might not be as costly as you are thinking to break out the masonry tiles and perhaps that would give you enough room for a 5.5 liner and insulation?

    (BTW, you'll need insulation also if you chimney is not up to snuff)

    Welcome to the site!

    pen
  3. RoderickSteiner

    RoderickSteiner New Member

    Joined:
    Jan 25, 2013
    Messages:
    7
  4. bryan

    bryan Member

    Joined:
    Aug 10, 2012
    Messages:
    99
    Loc:
    Wilmington, DE
    I'd definitely get a second or third opinion if they are free. I had 5 installers give me estimates for putting a liner in my chimney/fireplace. 3 said they do it and gave a reasonable price (though the local stove shop was a bit pricier than others), one said he wouldn't touch it due to safety hazards, and one wanted 5x what the other 3 said it would cost. In the end a CSIA sweep did the install for what seemed reasonable. It wasn't easy due to a couple bends but they got it done.
  5. pen

    pen There are some who call me...mod. Staff Member

    Joined:
    Aug 2, 2007
    Messages:
    7,020
    Loc:
    N.E. Penna
    For many stoves, a 5.5 inch liner, especially if it's a 25' straight shot, is just fine. Technically, while the flue collar is 6, if you look at where many collars hit the stove you'll see a slight lip of the top plate. If you measure in there, you'll often come up with 5.5, sort of making it an accepted loop hole. Or, you could call the stove company, ask about the situation, and get their blessing / disapproval if you'd like.

    I agree with Bryan, check around, and ask for specifics on what each company would like to do. If you aren't sure what they are talking about, then don't hesitate to ask here. Also, if you wanted to post a bunch of pics of what it is you are working with, we may be able to give you additional help/advice.

    pen
  6. RoderickSteiner

    RoderickSteiner New Member

    Joined:
    Jan 25, 2013
    Messages:
    7
    This is great advice. Thanks to you both. I'm going to go back to the retailer with this information, then maybe go to a competitor. I have a government coupon which limits the # of installers I can use, unfortunately. I'll come back with pics too.
  7. begreen

    begreen Mooderator Staff Member

    Joined:
    Nov 18, 2005
    Messages:
    46,997
    Loc:
    South Puget Sound, WA
    I'm wondering if you could use Duraliner 6". What is the inside dimension of the clay tile in the chimney?
  8. sailor61

    sailor61 Burning Hunk

    Joined:
    Nov 28, 2006
    Messages:
    112
    Loc:
    Warwick, RI
    It's likely pricey but what about the system where they put an inflatable bladder in the flue and then pump a lightweight concrete mix in around it? I know "This Old House" has used the method several times over the years - you could likely find more info on their website.
  9. RoderickSteiner

    RoderickSteiner New Member

    Joined:
    Jan 25, 2013
    Messages:
    7
    Interesting re. inflatable bladder, I'll look into it.

    re. Duraliner 6" if I understand correctly, you're asking the diameter of the space inside the chimney. I will check tonight and post some pics...
  10. jeff_t

    jeff_t Minister of Fire

    Joined:
    Sep 14, 2008
    Messages:
    3,500
    Loc:
    SE MI
    Clay tile liner? Bust them out.
  11. pen

    pen There are some who call me...mod. Staff Member

    Joined:
    Aug 2, 2007
    Messages:
    7,020
    Loc:
    N.E. Penna
    My boss just had his fireplace chimney redone w/ "The Bag" shoved down it for under 500. I was surprised as I thought it would have been more.

    pen
  12. RoderickSteiner

    RoderickSteiner New Member

    Joined:
    Jan 25, 2013
    Messages:
    7
    Pen, please tell me more. This is the inflatable bladder system sailor61 mentioned? That's cheaper than the liner.
  13. pen

    pen There are some who call me...mod. Staff Member

    Joined:
    Aug 2, 2007
    Messages:
    7,020
    Loc:
    N.E. Penna
    Yes, it's the same. It would only work if you have the room in your chimney to do it.

    Here's some info on it http://www.supaflu.com/

    The boss had this done by a chimney sweep that was local to him. Not sure if it was supaflu or not, but was a similar process.

    pen
  14. jeff_t

    jeff_t Minister of Fire

    Joined:
    Sep 14, 2008
    Messages:
    3,500
    Loc:
    SE MI
    Todd had this done to one of his chimneys.
  15. Excavator

    Excavator Burning Hunk

    Joined:
    Dec 18, 2011
    Messages:
    204
    Loc:
    Central NJ
    is the flue too small or is it just the damper to small.
    Damper just gets cut out to allow room, thats quite common
  16. mfglickman

    mfglickman Minister of Fire

    Joined:
    Jan 17, 2012
    Messages:
    676
    Loc:
    NW CT
    Lotta pellet stoves take a 4" liner. Kinda on the darkside, I know...but still, maybe an option. :)
    pen likes this.
  17. clemsonfor

    clemsonfor Minister of Fire

    Joined:
    Dec 15, 2011
    Messages:
    2,432
    Loc:
    Greenwood county, SC
    there is a thing that they hook to drills and they bust out the clay flue tiles and then they pull them out from the bottom and this will give you another inch easy to pull that 6" liner through. I think 8" square tiles are the smallest right?
  18. DIY_HOME

    DIY_HOME New Member

    Joined:
    Nov 13, 2012
    Messages:
    6
    Hello RoderickSteiner,

    Do you have any pictures you could post?
    I've spoken with the chimney technicians from Rockford Chimney about my particular chimney setup. Very helpful. I'd recommend asking for their opinion, I'm sure they have experience with these types of questions.
    www.rockfordchimneysupply.com

    Hope this helps you.
  19. fraxinus

    fraxinus Feeling the Heat

    Joined:
    Aug 3, 2007
    Messages:
    331
    Loc:
    coastal Maine
    I don't know about availability or code issues in your area, but a cast in place liner would seem to be an excellent option. SupaFlu is one (www.supaflu.com) which I used myself several years ago. I know there are others - try Googling "cast in place chimney liner".

    Again, it's been several years, but at the time of my own installation, Supaflu was very competitive in price with a metal liner. Other advantages are: No need for the mess and potential for damage involved in breaking out the old tiles. Insulation is a part of the mixture itself. Greatly improved draft due to the smooth interior surface. Strngthens the entire chimney because it becomes an integral part of the structure.

    Hope this will help.
  20. TheBaron

    TheBaron New Member

    Joined:
    Dec 27, 2012
    Messages:
    88
    Loc:
    Eastern ON, Canada
    We just had a Jotul insert put in to our house. We are in Ontario, but similar code to Quebec (same source code). We have 8" flue tile in our house (about 20') and we needed to use a 6" uninsulated SS liner to get it to fit. They see this all the time where we live, so it didn't cause any fuss when they saw our existing chimney. The brand they used was a magnaflex, and it came with the US and Canadian approvals for woodburning. It was a kit that came with the cap and other stuff.

    They sell the pipe at Northline Express, but for some reason they don't carry the kit (for the single wall non-insulated flex liner)
    http://www.northlineexpress.com/chi...ney-liner/6-inch-magnaflex-chimney-liner.html
  21. clemsonfor

    clemsonfor Minister of Fire

    Joined:
    Dec 15, 2011
    Messages:
    2,432
    Loc:
    Greenwood county, SC
    I got my liner kit at chimney liner depot for 20ft6" you should be around $300 shipped.
  22. RoderickSteiner

    RoderickSteiner New Member

    Joined:
    Jan 25, 2013
    Messages:
    7
    Here, finally, are a couple pictures. Best I could do with my phone...

    The first is the view in from the outside, the second is looking upwards. IMAG0096.jpg IMAG0097.jpg
  23. RoderickSteiner

    RoderickSteiner New Member

    Joined:
    Jan 25, 2013
    Messages:
    7
    Thanks everyone for your help; sorry it took so long for me to get back to everyone.

    It's the flue that's too small, according to the company.

    I did not know that...something to consider, but I'd much rather find a way to get the wood stove...


    Interesting. Yes, I feel like this is the most legit option that won't cost an arm and a leg. Too bad my mason hasn't shown up yet to give me a quote. I will let you guys know what he quotes me.

    Thanks! These guys seem to really know what they're doing. I'll give them a ring, depending on what the mason says.

    My concern with a supaflu style set-up is that it still won't leave enough room for smoke to escape. Unless I remove the tiles first.

    When you say 8" flue tile, what does the 8" refer to? Sounds like what you are describing is what my company wanted to do, but there wasn't enough room. Am I understanding you correctly?