    50 cords a year, WOW hope there's warranty on the door hinges, cuz thats alot of wood.
     

    Helpful Sponsor Ads!





  2. DaBackBurner

    DaBackBurner
    Expand Collapse
    Member

    Joined:
    May 11, 2010
    Messages:
    84
    Likes Received:
    0
    Loc:
    UP Michigan
    Two is prettier than one. Love it...keep the pictures coming.

    Como-estas and Como-tose
     
    Collapse Signature Expand Signature
  3. Como

    Como
    Expand Collapse
    Minister of Fire

    Joined:
    Jan 28, 2008
    Messages:
    885
    Likes Received:
    16
    Loc:
    Colorado
    [​IMG]

    So most of the rear plumbing has been done. Snow tonight, Wednesday and Thursday looking good.

    You may be wondering what happened to the white stuff, we had nearly 2 weeks of violent winds. They closed US285 for most of yesterday.

    The panels for the structure arrived last Wednesday whilst my original idea was to off load them onto the slab, the wind suggested otherwise.

    I am going to wrap them initially with Roxul, then if needed will blow in insulation to fill the area leaving access for the pumps.
     
    Collapse Signature Expand Signature
  4. bioman

    bioman
    Expand Collapse
    Feeling the Heat

    Joined:
    Dec 25, 2010
    Messages:
    335
    Likes Received:
    124
    Loc:
    Central Missouri
    Looks really good David. good job !
     
  5. Sawyer

    Sawyer
    Expand Collapse
    Minister of Fire

    Joined:
    May 17, 2008
    Messages:
    608
    Likes Received:
    6
    Loc:
    Northern WI
    Something about a pair that is really impressive! Looking forward to the next update.
     
    Collapse Signature Expand Signature
  6. Como

    Como
    Expand Collapse
    Minister of Fire

    Joined:
    Jan 28, 2008
    Messages:
    885
    Likes Received:
    16
    Loc:
    Colorado
    Well we have hit a glitch, delayed us a few days. Plus the wind last week kept blowing the plumbers torch out. We are still unseasonally warm, have not been below 0F for a few weeks.

    One thing I did not know, never seen it mentioned here or in the documentation, and which I will pass on is that when you have more than one Garn they should be operated together. My original plan was to operate both in Winter and one or the other in Summer.

    Also you will see that each Garn had its own Pump, there must be one pump for all the Boilers.

    Hopefully this will help anybody else considering a similar set up.
     
    Collapse Signature Expand Signature
  7. bpirger

    bpirger
    Expand Collapse
    Minister of Fire

    Joined:
    May 23, 2010
    Messages:
    632
    Likes Received:
    28
    Loc:
    Ithaca NY Area
    Wouldn't that just depend on how they are plumbed? So if you plumbed them both separately as a secondary supply into a primary loop, couldn't you then feed the primary either from Bert, or Ernie, or both? I don't see why you have to burn them both all the time....why would they know the other is present?

    As for names, do you have two dominate peaks visible from your location? Everest and K2? And yes, I know you can't see them. :)
     
    Collapse Signature Expand Signature
  8. DaBackBurner

    DaBackBurner
    Expand Collapse
    Member

    Joined:
    May 11, 2010
    Messages:
    84
    Likes Received:
    0
    Loc:
    UP Michigan
    Why is that David? I've seen and read about multiple boiler staging but these were standard boilers without storage. Each boiler was plumbed in parallel into a large header loop (boiler loop) with each boiler having its own pump. The primary loop was hydraulically separated from the boiler loop either with closely spaced 'T' or hydraulic separator, as was the secondary loop(s). Not quite understanding why you couldn't do this. You would have to wait until say Garn2 was up to temp to have any benefit of adding BTU output to the boiler loop but that seems doable.
     
    Collapse Signature Expand Signature
  9. Como

    Como
    Expand Collapse
    Minister of Fire

    Joined:
    Jan 28, 2008
    Messages:
    885
    Likes Received:
    16
    Loc:
    Colorado
    Well the guy who designed the system, all now operational ex Garn's, is now retired but has done thousands of systems. But not Garn's.

    The info came from the top at Dectra.

    Apparently with Garn's that is just the way it is, obviously with other Boilers, like my Triangle Tube, cascading systems are normal.

    Anyway I had to get the W2's out and I still have year end accounts etc etc, so I will get it done the recommended way. I know we will get hit with bad weather soon.
     
    Collapse Signature Expand Signature
  10. PassionForFire&Water

    PassionForFire&Water
    Expand Collapse
    Minister of Fire

    Joined:
    Jan 14, 2011
    Messages:
    624
    Likes Received:
    120
    Loc:
    Billerica, MA
    Very interesting.
    Would love to learn the details why staging or cascading is not possible with Garns.
     
    Collapse Signature Expand Signature
  11. jebatty

    jebatty
    Expand Collapse
    Minister of Fire

    Joined:
    Jan 1, 2008
    Messages:
    5,203
    Likes Received:
    659
    Loc:
    Northern MN
    Would like to know the reason why they cannot be operated separately. I'm aware of a Garn WHS3200 and a Wood Gun E500 both plumbed into a primary loop, each can be operated separately or both together. Garn raised no issue with this installation. The primary loop also has plumbed into it a 4000 gallon pressurized storage tank which operates as a hydraulic separator. Since the system is pressurized, the Garn connects via a plate hx.

    One beauty of this system is that, in effect, 7200 gallons of storage are available, as the Garn or the Wood Gun operating separately or both together have available total system storage.
     
    Collapse Signature Expand Signature
  12. Como

    Como
    Expand Collapse
    Minister of Fire

    Joined:
    Jan 28, 2008
    Messages:
    885
    Likes Received:
    16
    Loc:
    Colorado
    I think in the particular comparison my Triangle Tube is in a similar position to the Wood Gun.

    Except my storage is less than 200 gallons.
     
    Collapse Signature Expand Signature
  13. bioman

    bioman
    Expand Collapse
    Feeling the Heat

    Joined:
    Dec 25, 2010
    Messages:
    335
    Likes Received:
    124
    Loc:
    Central Missouri
    I'd send one back and just hook up 2000 Gal storage and never look back. i think you've been sucked in to GARNAMONIOUS. MHO.
     
  14. Frozen Canuck

    Frozen Canuck
    Expand Collapse
    Minister of Fire

    Joined:
    Dec 14, 2009
    Messages:
    858
    Likes Received:
    100
    Loc:
    North central Alberta, Canada
    I think you will find after reading some of David's posts that he did his research, established his loads, weighed his options, investigated boiler models that worked for his situation & then made his choice.
    Far from being sucked in as you put it.
    David: as far as I can tell from your post & this thread there is no reason that one could not run those 2 boilers however you choose.
    One at a time, both at once, alternating, whatever you want.
    The only restriction would be how it's plumbed & pumped.
    Unless of course the is some funky monkey regulation in your state preventing that?
    Again, wide open to being corrected on that.
     
    Collapse Signature Expand Signature
  15. jebatty

    jebatty
    Expand Collapse
    Minister of Fire

    Joined:
    Jan 1, 2008
    Messages:
    5,203
    Likes Received:
    659
    Loc:
    Northern MN
    David says that the info that they cannot be run together --
    In my experience if Dectra says something and if an owner does something contrary, then Dectra may take the position that the warranty is void.
     
    Collapse Signature Expand Signature
  16. bigburner

    bigburner
    Expand Collapse
    Feeling the Heat

    Joined:
    Aug 28, 2010
    Messages:
    438
    Likes Received:
    4
    If it was me lecturing a class on best design practice with equipment that has wildly different operating potential based on load size and quality. Then I would instruct that for that reason it wouldn't shouldn't be connected like a tandem gas boilers. [like in the picture] That the proper way would be let each unit operate independent as possible and then contribute to the system. In this case make each boiler a secondary contributor to the primary loop around the HX. Each heat source should not be effected by the other, projects in the past have connected, geothermal, gas and wood all to the same system.
     
  17. maple1

    maple1
    Expand Collapse
    Minister of Fire

    Joined:
    Sep 15, 2011
    Messages:
    6,448
    Likes Received:
    1,117
    Loc:
    Nova Scotia
    It would be interesting to know exactly what the issue they are seeing is, though.
     
    Collapse Signature Expand Signature
  18. Como

    Como
    Expand Collapse
    Minister of Fire

    Joined:
    Jan 28, 2008
    Messages:
    885
    Likes Received:
    16
    Loc:
    Colorado
    [​IMG]

    [​IMG]

    These are the two options
     
    Collapse Signature Expand Signature
  19. leaddog

    leaddog
    Expand Collapse
    Minister of Fire

    Joined:
    Sep 24, 2007
    Messages:
    913
    Likes Received:
    4
    Loc:
    Hesperia, Michigan
    I don't see it but I'm sure that you can have shutoff valves so you can shut one or the other down and just run one. You would want to be able to balance them out also. That setup would save pumps and other plumbing.
    leaddog
     
    Collapse Signature Expand Signature
  20. bioman

    bioman
    Expand Collapse
    Feeling the Heat

    Joined:
    Dec 25, 2010
    Messages:
    335
    Likes Received:
    124
    Loc:
    Central Missouri
    I would have to agree with leaddog on this +1.
     
  21. Como

    Como
    Expand Collapse
    Minister of Fire

    Joined:
    Jan 28, 2008
    Messages:
    885
    Likes Received:
    16
    Loc:
    Colorado
    We re plumbed it today, I have some weather coming in so have prep'd enogh wood for the stoves for a week.

    Put some extra valves in, just in case.
     
    Collapse Signature Expand Signature
  22. Sawyer

    Sawyer
    Expand Collapse
    Minister of Fire

    Joined:
    May 17, 2008
    Messages:
    608
    Likes Received:
    6
    Loc:
    Northern WI
    Glad to see you are making progress David. I am sure you are very anxious to fire up efficiently!
     
    Collapse Signature Expand Signature
  23. maple1

    maple1
    Expand Collapse
    Minister of Fire

    Joined:
    Sep 15, 2011
    Messages:
    6,448
    Likes Received:
    1,117
    Loc:
    Nova Scotia
    I am thinking the Garn people might have issues with using shut off valves to isolate one of two boilers, as they could see potential for someone to light a fire and forget to open valves - which would be a bad thing. Just a thought.
     
    Collapse Signature Expand Signature
  24. heaterman

    heaterman
    Expand Collapse
    Minister of Fire

    Joined:
    Oct 16, 2007
    Messages:
    3,348
    Likes Received:
    617
    Loc:
    Falmouth, Michigan
    ^ That wouldn't really be an issue. It is impossible to "overheat" a Garn and a full fire with no circulation is no cause for alarm. The worst case scenario would be stoking one up when the tank is already at 190-200 and literally bringing all the water to full boil. At that point one would have a neighborhood sized sauna stove going in the building but nothing more.
     
    Collapse Signature Expand Signature
  25. maple1

    maple1
    Expand Collapse
    Minister of Fire

    Joined:
    Sep 15, 2011
    Messages:
    6,448
    Likes Received:
    1,117
    Loc:
    Nova Scotia
    Well in that case, I'm more curious as to why they rule out running one at a time in a dual install.
     
    Collapse Signature Expand Signature