    I (will) have an EVL of 28 (22 vertical=12, 3 90's=15, 1 horizontal=1). I am using 4 inch piping by Selkirk and 20 feet of the vertical is up and out of the chimney (the other 2 feet is nside the house). Do you think I will have issues? I will run an OAK. It's a basement (finished) install and I am hooking into an existing chimney (masonry) at it's lowest point (which is above the stove). Sort of like this...

    pellet_stove_1.gif
     
  2. DexterDay

    DexterDay
    Guest 2.
    NULL
    

    If using 4" all the way? Then I say your fine. . The EVL is actually a lil under 28. It comes in at 27.
    22' vert= 11
    3- 90° = 15
    1' horz = 1
    27 total.

    Mike Holton would be the man to ask about this. Being its an Englander and he is the Englander "Man"!

    Even being a finished basement, you may not get the results your looking for upstairs?
     
  3. RightSeatCessna

    RightSeatCessna
    New Member 2.
    NULL
    

    Oct 1, 2012
    79
    2
    Loc:
    Saco, Me
    It's a split level/raised ranch 2100 finished (1200 upstairs, 900 downstairs). I am going to run a fan above the mantle to blow the air towards a relatively large stairwell open upstairs. Of I could install a couple of heat registers...
     