I have been looking at this picture all day....... Your danfoss should be right at your boiler so the hot water can circulate around your boiler preheating your boiler water. Then the bypass loop slowly opens your danfoss valve to mix with hot water to stay above 140* If you let your boiler go cold you have 50' of cold water to heat up along with whats in your boiler.
On to your piping. It looks like it could go right past your storage and circulate thru your secondary and right back to your boiler causing it to go into idle while not hardly charging your tank.
I am unfamiliar with a injector??? does this take water from your primary and force it into the tank?
It also looks like your return from bottom of tank is tied into your primary?
My primary goes into the top of my tanks
I then pull off the top of tank with a pump to my hx and my flat plate for DHW
I then return to middle of tanks with dip tubes.
my returns to my boiler come off the bottom of the tanks
at my boiler I have the return water coming in thru a danfoss, thru a pump,then thru boiler back to tanks.
Rob
On to your piping. It looks like it could go right past your storage and circulate thru your secondary and right back to your boiler causing it to go into idle while not hardly charging your tank.
I am unfamiliar with a injector??? does this take water from your primary and force it into the tank?
It also looks like your return from bottom of tank is tied into your primary?
My primary goes into the top of my tanks
I then pull off the top of tank with a pump to my hx and my flat plate for DHW
I then return to middle of tanks with dip tubes.
my returns to my boiler come off the bottom of the tanks
at my boiler I have the return water coming in thru a danfoss, thru a pump,then thru boiler back to tanks.
Rob