Depends. Is it a metric boiler in a metric shed? Is the area zoned as information-free?OK let me refraise my question. How large of a boiler can be used in a shed?
Pulse... Tell us what your thinking/what kind of boiler you want ect. I have a set up like you might be thinking about.Sorry, I don't know enough to ask an intelligent question. 150 feet one way 1" logstor, is really all I know. I just don't see how I could supply the house, dhw, and garage at the same time while maintaining boiler protection, let alone have anything left for storage. Just trying to educate myself.
A couple of basics may help you evaluate your problem. 1 BTU is the heat necessary to heat one pound of water 1 degree F. Water weighs 8 pounds per gallon. If you pump 10 gallons per minute, that's 8 pounds of water per gallon times 10 gallons per minute times 60 minutes per hour or 4800 pounds per hour. If you have a 10 degree difference between your supply and return temperatures, that is 48000 BTUH.How many btu's can be effeciently pushed through 1" pex?
Pump and tube sizing starts with knowing the actual load (btu's) that has to be carried. The next step is evaluating your heat emitters in terms of how much temperature drop they will create. Basically speaking, the more temp drop you can create the fewer gallons you have to flow.
Once you get a handle on those two things the tube as well as pump size become a stationary target that is easy to hit.
Where in Michigan are you located?
SW lower.
Well here is what I know with my current setup. The pump on my boiler is a bell and gosset pl30 pushing through 300'(round trip) 1" logstor and pex(inside) to 3 seperate hx's. I also know I need my water to be at least 150* to heat the house.
These delta t's were taken with an ir thermometer so may not be perfect but should be close. The first is a 20plate for my dhw which pulls about 12 degrees, second is a 140K(rated)water/air that pulls 25 degrees. I only keep my garage around 55 so that hx runs very little. I think it is only rated at 40k @ 180*.
My backup heat is a forced air oil burner. On what I would consider a normal winter day (highs) in the 20's, lows in the teen's, my house alone will use 8 gallons of fuel. So if I figure right I come up with 35kbtu/hour for the house.
Like I said, I am happy with everything with my current setup except for the wood consumption. The problem is my owb has made me lazy as far as tending the fire. Now that I am lazy, I refuse to go backwards, meaning I put wood in at 5:00pm and don't do anything with the owb until 9:00 am the next day. So a system requirement for me, is that it has to be able to go for at least 16 hours even during our coldest nights. The other night we were down to -10 most of the night. I have no idea what the btu requirement is at that temp but it has to be more than 35k.
What I want to know is if that is possible with the underground pipe I currently have, using a boiler in a shed and 1000 gallons of storage in the basement. I don't want to go outside at 11:00pm to top off the boiler so it makes it through the night, both for heat and hot showers in the morning! Thanks for any and all comments.
Are the heat exchangers all in series or are they separate loops/individual pumps to each running off your main?
What is the ID of the log store 1" pipe?
Many of these Pex pipes have a 3/4" or 7/8" ID and thus when compared to a 1" ID there is quite a difference.
Here's what I can deduce from your information. House backup uses 8 gallons of oil at 136,000 btu per gal = 1,088,000 BTU/day.That's about 45K per hour average. I'm assuming that's both heat and hot water on a normal day. Say a normal day average is 15 to 65 degrees or 50 degrees delta T. -10 to 65 would be 75 delta T or 50 percent more demand on average. To get average day heat of one million plus BTUs you need to burn 200 pounds of dry wood at 90 percent efficiency. The buffer storage is effective only over the temperature drop you tolerate. For example 170 to 140 would be 30 degree times 8 lbs per gallon times 1000 gallon or 240,000 BTU's. Assuming you have your storage peaked out before you load at 5pm, then if your total need is 45K per hour then the storage buys you 5 of the 16 you are looking for. The other thing you can deduce is if your average temperature drop in your house heat exchanger is 25 degrees and the average draw is 35000 btu/hour, and since 1 GPM equals 480 pounds per hour, then 35K divided by 25 divided by 480 =3 GPM. These are of course all averages based on your info but it puts you in the ballpark. Hope this helps you evaluate you system and your expectations.SW lower.
Well here is what I know with my current setup. The pump on my boiler is a bell and gosset pl30 pushing through 300'(round trip) 1" logstor and pex(inside) to 3 seperate hx's. I also know I need my water to be at least 150* to heat the house.
These delta t's were taken with an ir thermometer so may not be perfect but should be close. The first is a 20plate for my dhw which pulls about 12 degrees, second is a 140K(rated)water/air that pulls 25 degrees. I only keep my garage around 55 so that hx runs very little. I think it is only rated at 40k @ 180*.
My backup heat is a forced air oil burner. On what I would consider a normal winter day (highs) in the 20's, lows in the teen's, my house alone will use 8 gallons of fuel. So if I figure right I come up with 35kbtu/hour for the house.
Like I said, I am happy with everything with my current setup except for the wood consumption. The problem is my owb has made me lazy as far as tending the fire. Now that I am lazy, I refuse to go backwards, meaning I put wood in at 5:00pm and don't do anything with the owb until 9:00 am the next day. So a system requirement for me, is that it has to be able to go for at least 16 hours even during our coldest nights. The other night we were down to -10 most of the night. I have no idea what the btu requirement is at that temp but it has to be more than 35k.
What I want to know is if that is possible with the underground pipe I currently have, using a boiler in a shed and 1000 gallons of storage in the basement. I don't want to go outside at 11:00pm to top off the boiler so it makes it through the night, both for heat and hot showers in the morning! Thanks for any and all comments.