I am planning on installing a supplemental wood burning furnace in my basement. The wood burner furnace recommends 6” pipe for smoke stack (28 sq. inch draft).
I have a 32 ft. tall brick chimney that has a clay liner in good shape with what appears to be 6”x 10” inner measurements. The gas furnace is now PVC vented separately so most of brick chimney is unused, but an uninsulated 4” flexible pipe currently runs up chimney for hot water heater.
While measuring for chimney liner length, I discovered chimney also has a “witches bend” midway, it appears to be just a couple inches bend – just enough to make life difficult. I tried inserting a 6”diameter plastic windshield washer jug down chimney to check fit and it was very tight even in first few feet, so a 6” round flexible liner is out of the question.
I believe my choices are:
Any recommendations?
I have a 32 ft. tall brick chimney that has a clay liner in good shape with what appears to be 6”x 10” inner measurements. The gas furnace is now PVC vented separately so most of brick chimney is unused, but an uninsulated 4” flexible pipe currently runs up chimney for hot water heater.
While measuring for chimney liner length, I discovered chimney also has a “witches bend” midway, it appears to be just a couple inches bend – just enough to make life difficult. I tried inserting a 6”diameter plastic windshield washer jug down chimney to check fit and it was very tight even in first few feet, so a 6” round flexible liner is out of the question.
I believe my choices are:
- Not installing a flexible pipe for wood burner and simply using existing clay lined chimney. The result is almost 70% larger opening than recommended for wood burner (47.5 sq. inch draft - based on 6”x10” less 12.5” for 4” pipe).
- Installing a 5.5” flexible pipe (23.75 sq. inch draft) – which may or may not make it past bend in chimney.
- Installing a 5” flexible pipe (19.6 sq. inch draft) – which has a pretty good chance of making it past chimney bend.
- Installing solid 6” chimney liner pipe up from basement for 20 feet (up to chimney bend) and letting last 12 feet vent through current clay liner (47 sq. inch remaining opening for draft). Not sure if this is a viable solution, but it seems like the draw would be well established after 20 feet of vertical pipe and less likely for flue gases to condense or back draft.
Any recommendations?