another heat delivery pipe thread

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Hope everyone has a wonderful and warm Thanksgiving!
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here
Status
Not open for further replies.

mikeyny

Feeling the Heat
Hearth Supporter
Nov 16, 2007
294
upstate ny
I was just wondering How much pipe diameter has to do with boiler performance when it is coming in from the outdoors. I know most folks have their pipes buried. I realize there are many different ways to insulate and bury, water proof and protect pipe coming in from an outdoor boiler, but what size is best? my system is 2 inch iron pipe well insulated above ground. Is 2 inch overkill. Is 3/4 too small. It must make a difference in the final performance for a system. The only reason mine is 2 inch is because it was free. The boiler manufacturers must have some recommendation as to what size is right for each system. Is there a simple rule of thumb??
Mike
 
Mikeyny - I was talking with the Tarm guys today about this, and they recommended either 2" iron or a double run of 1" pex to link an outside boiler to a basement storage tank. Sounds like you're all set with the free iron.
 
Hi,Long time lurker here. First post of many to come I am sure. My question concerns the actual tapping of the boiler. What size is the Tarm ? My concern is my existing manifold and monoflow loop size. It is 1 1/4" How does one one inch pex loop keep the 1 1/4" fully charged ?
Will
 
the tapping on my older tarm are 1 and a quarter. It bush's up to 2 inch and I have no problem that i know of with flow.
 
It's not a matter on the size of your connections, it's boils down to how many GPM can a specific pipe size accomadate at what velocity so as not to cause interior pipe erosion. Generally if you can be under 7' a second in velocity you'll be safe. The other factor that plays into the equation
is the fluid & friction loss thru a pipe. Is it 100% water or a gycol mixture, this effects friction loss thru pipe.

Personally I wouldn't recommend over 12 GPM thru 1" (120,000 BTU's per hr) but the charts do say you can do 25 GPM (250,000 BTU's per hr) thru 1" at 7' a second in velocity however you are out of the "normal design range". We try to engineer everything to be under 3.5' per second.

I think this is one of the reasons why so many OWB installations limp along, small diameter pipe and water flowing to quickly to transfer the heat.
 
solarguy said:
Made an oops...

I wouldn't exceed 5' a minute in velocity thru any size pipe for a heating application.
This would put 1" pipe at 17 GPM, 170,000 BTU's per hr.

Please tell me you meant 5' per second?
 
The tappings on my Tarm 40 are 1 1/4".
 
/Pipe sizing depends on a few factors. The type of fluid, the temperature, delta T and acceptable velocities.

Typically we design around a 20 degree delta T, with water at 180F.

For continous use hydronic systems 4 feet per second is an industry standard. DHW pipe sizing will often use 8 FPS in their tables.

Oversizing the pipe will slow the speed of the fluid. Below 2 FPS the fluid will not carry the air along to purge. Target 4 FPS.

Here is a table based on 4 FPS, 20F delta T.

1" pex is commonly used in OWF piping. 7.5 is a safe flow rate for that tube or 75,000 BTU/ hr.

Some of the PAP, like Kitec has a larger id. Figure 10- 11 GPM through that tube, about the same as 1" copper tube.

Larger delta t would allow more heat to be moved. if you can design around a 40 delta t you can move twice the energy through the same size tube.

If you have a buffer tank for example and pull a mix down radiant temperature off that, a 40F delta T can be used.

I suspect most OWF installations with a 1" pex (one size fits all) and a high head Taco circ probably run some fairly high velocities. if the system is fitting free you may get away with that for some time.

hr
 

Attachments

  • [Hearth.com] another heat delivery pipe thread
    MVC-038F.webp
    34.7 KB · Views: 495
Thanks guys for the answers.Thread is copied into my hydronics folder for continued reference. I am in the planning stage for my boiler set up for next winter. A load of wood coming will be the first actual step to begin my project.
Will
 
Welcome to the Boiler Room, Will. What kind of boiler are you planning to get?
 
Hi Eric, I have been checking out all the gasifier boilers. So far no firm choices. I will keep reading all the threads. IMHO the piping, pumping (distribution), control and storage strategy is what makes or breaks an installation. I have some books by Dan Holohan that describe very well all things hydronic. The boiler is the big item though.
 
Good move with the Dan Holohan books.
 
Status
Not open for further replies.