Hello
Working on the Castle HPS10 stove. The fire is dies soon after the start cycle. Checked hose and vacuum switch, even tried a new vacuum switch. Fire still dies.
Therefore I put the Manometer on the vacuum port which goes into the back of the fire box on the right side. The reading was only -0.29 WC during the start up cycle! ! !
The Vacuum switch is set for approx -0.25 WC so there is not enough air pressure to keep the stove going.
The manual only mentions there is an exhaust cleanout plate, I pulled the exhuast fan when I cleaned it and cleaned that area.
I left a message with Ardisam and they left a message on my phone stating there is a known issue of the exhaust chamber being plugged! Ah Ha !
So I will ask for a procedure Monday but in the meantime I noticed 2 slots in the fire box up high on each side of the heat exchanger. Similar to the BabyCountryside only the slots are larger.
So does anynone have any ideas on cleaning? I know the leaf blower trick but cannot make a mess outside.
There does not look like there is a horizontal chamber, just 2 vertical chambers. Unlike the Baby CountrySide it looks like these chambers do Not drop into the ash pan! This may explain the extreme clog up.
What about putting the shop vac up to the open exhaust blower plenum cleaning cover? (See part# 10 in exploded view) Then blasting each of the chambers with 150 PSI of compressed air?
Pic 1 - Manometer shows -0.28 WC
Pic 2 - Shows Ardisam vacuum switch
Pic 3 - Ardisam vacuum switch with yellow arrow that shows it is set for approx 0.25
Pic 4 - Shows exploded view with red arrow pointing to exhaust blower cleanout cover part # 10
Working on the Castle HPS10 stove. The fire is dies soon after the start cycle. Checked hose and vacuum switch, even tried a new vacuum switch. Fire still dies.
Therefore I put the Manometer on the vacuum port which goes into the back of the fire box on the right side. The reading was only -0.29 WC during the start up cycle! ! !
The Vacuum switch is set for approx -0.25 WC so there is not enough air pressure to keep the stove going.
The manual only mentions there is an exhaust cleanout plate, I pulled the exhuast fan when I cleaned it and cleaned that area.
I left a message with Ardisam and they left a message on my phone stating there is a known issue of the exhaust chamber being plugged! Ah Ha !
So I will ask for a procedure Monday but in the meantime I noticed 2 slots in the fire box up high on each side of the heat exchanger. Similar to the BabyCountryside only the slots are larger.
So does anynone have any ideas on cleaning? I know the leaf blower trick but cannot make a mess outside.
There does not look like there is a horizontal chamber, just 2 vertical chambers. Unlike the Baby CountrySide it looks like these chambers do Not drop into the ash pan! This may explain the extreme clog up.
What about putting the shop vac up to the open exhaust blower plenum cleaning cover? (See part# 10 in exploded view) Then blasting each of the chambers with 150 PSI of compressed air?
Pic 1 - Manometer shows -0.28 WC
Pic 2 - Shows Ardisam vacuum switch
Pic 3 - Ardisam vacuum switch with yellow arrow that shows it is set for approx 0.25
Pic 4 - Shows exploded view with red arrow pointing to exhaust blower cleanout cover part # 10