Just swapped out my Mom's 30gal electric HW heater this weekend. It's a simple dual element unit labeled GE, but made by Rheem. I got concerned when the install manual noted a 50A CB was required, yet the existing CB in the panel has been a 30A forever.
My calculator said that two 4500w elements (9000 total) would indeed draw 37amps, so I disconnect one of the elements for the "light off". Everything is fine, but when I start playing with my multimeter I realize that the upper thermostat controller only allows one element ON at a time. The Heater has upper and lower t-stat settings, but the upper t-stat sends voltage to only the upper element until it is satisfied. Then the upper stat shuts off the upper element, and sends voltage to the lower stat/element combination. The lower element then runs until its stat is satisfied.
The electric schematic in the install manual seems to back this up. So my question is: Do all electric HW heaters work this way, ie only let one element operate at a time?
Next question is: What is the best temp setting for the upper and lower t-stats (same or different)?
Third question: Why would the install manual's electrical table require a 50 amp breaker (romex wire for that costs a fortune per foot), when the WH will never use more than 19 amps (for one element)?
My calculator said that two 4500w elements (9000 total) would indeed draw 37amps, so I disconnect one of the elements for the "light off". Everything is fine, but when I start playing with my multimeter I realize that the upper thermostat controller only allows one element ON at a time. The Heater has upper and lower t-stat settings, but the upper t-stat sends voltage to only the upper element until it is satisfied. Then the upper stat shuts off the upper element, and sends voltage to the lower stat/element combination. The lower element then runs until its stat is satisfied.
The electric schematic in the install manual seems to back this up. So my question is: Do all electric HW heaters work this way, ie only let one element operate at a time?
Next question is: What is the best temp setting for the upper and lower t-stats (same or different)?
Third question: Why would the install manual's electrical table require a 50 amp breaker (romex wire for that costs a fortune per foot), when the WH will never use more than 19 amps (for one element)?