My home was built in 1998. On the upper level of the two levels, the HVAC installer placed return air vents on the floor and also high on the walls. One large one in the ceiling even.
The other day I was staring at the medium sized return in the master bedroom which is high on the wall. I was wondering if there was any leakage into the attic. This is the room that is hardest to move the stove heat into. It is larger and vaulted.
I first measured the vent temperature with the IR handheld and to my surprise it was warmer than the adjacent wall temp by 4 degrees. So I went and got a piece of plastic wrap, the kind used for leftover food. As I moved it over the vent it literally sucked up against the opening. A few minutes later I measure the temp and it had cooled off to match the adjacent wall.
I then went to the high return in the ceiling of my dinning room. It is large and was almost 5 degrees warmer than the adjacent wall. When I placed wrap over it, the suction was even greater.
The remaining high return is in a wall that does not go to the ceiling. There was no temp difference there so I did not cover it.
There are plenty of floor returns on both levels so blocking these is not going to overwork my fan blower which almost never runs in the winter anyway.
I did this two days ago. I have noticed that the house has been a couple degrees warmer than usual in the morning.
MnDave
The other day I was staring at the medium sized return in the master bedroom which is high on the wall. I was wondering if there was any leakage into the attic. This is the room that is hardest to move the stove heat into. It is larger and vaulted.
I first measured the vent temperature with the IR handheld and to my surprise it was warmer than the adjacent wall temp by 4 degrees. So I went and got a piece of plastic wrap, the kind used for leftover food. As I moved it over the vent it literally sucked up against the opening. A few minutes later I measure the temp and it had cooled off to match the adjacent wall.
I then went to the high return in the ceiling of my dinning room. It is large and was almost 5 degrees warmer than the adjacent wall. When I placed wrap over it, the suction was even greater.
The remaining high return is in a wall that does not go to the ceiling. There was no temp difference there so I did not cover it.
There are plenty of floor returns on both levels so blocking these is not going to overwork my fan blower which almost never runs in the winter anyway.
I did this two days ago. I have noticed that the house has been a couple degrees warmer than usual in the morning.
MnDave