Built better in the good old days of 1965? Hah! My scary chimney....long story.

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.
  • Hope everyone has a wonderful and warm Thanksgiving!
  • Super Cedar firestarters 30% discount Use code Hearth2024 Click here
Status
Not open for further replies.

elmoleaf

Feeling the Heat
Hearth Supporter
Dec 11, 2007
432
Southeastern Massachusetts
Here's a pic looking up inside my chimney (built in 1965, split-entry house), taken from the basement cleanout.
First, a brief description of the pic: On the left, you'll see the shiny metal flue pipe of the oil-fired boiler poking in (about 5' above the basement floor). Higher up, there's the begining of the clay liner for the boiler flue. To the right is the underside of the fireplace hearth. The small rusty metal square is the former ash-dump for the fireplace (the rusty piece is formwork below a cement plug in the hearth that closes the dump hole). I think the large black square farther over is some sort of metal plate supporting some of the hearth floor construction. Far to the right is a lame corbel supporting the outside wall of the chimney above. Then, this giant ash dump widens to the right for no apparent purpose (the base of the chimney is 4'-9" across, outside dimension). The only access into this giant ash dump is a 7X9 interior cleanout door located on the far left, below the boiler flue area. Obviously not visible is the fireplace flue.

I've had many WTF moments with this chimney, going back to 1992 when I bought this house.
I wish I could find the clown that built this thing or the inspector that allowed it. GRRRRRRRRRRR.

When we bought the house, the very diligent home inspector never noticed any problems. We were lucky we didn't die in our sleep. I woke up one morning to discover that the loose piece of sheet metal lying across the ash dump had moved. Stupid me didn't figure it out and shoved it back over the hole. We were lucky to live through another night. When I found the ash dump open again, I got smarter. Down to the basement I went and opened up the metal ash dump door. WTF! $%@#!. There were some pieces of CMU block obstructing the opening. Apparently, the mason used these as a "temporary" aid to hold up the end of the block above while building the wall. I got a hammer and bashed them out in anger. Had the previous owner in 25+ years never opened the cleanout? Why didn't I look when buying the house? WTF!

I shined my flashlight into the opening. What the h#$#@ is that? Brownish tan? Angled? I shoved a hand in and pushed. It moved. Why on earth is there a big piece of clay flue liner sitting loose in my ash dump? Why is my ash dump so freaking big? I shoved the liner to the side and held my mirror and light inside the opening. I began mumbling curse words endlessly. I had discovered the first problem. The boiler was exhausting into a big space, and then up one flue and also into the house through the fireplace ash dump (the fireplace was without glass doors and had a metal damper closing the flue above). Crap. I got some cement and permantly blocked the fireplace ash dump so we wouldn't die from carbon monoxide poisoning.

Apparently the loose piece of flue liner I found had fallen from the boiler flue. It presumably had been held up by nails at the height where the metal boiler flue enters the chimney. As you can see in the picture, there's no corbeling to support the piece of boiler flue that fell.

Scared, I decided to investigate the fireplace flue up on the first floor. Looking up at the top of the smoke chamber, I saw rusty nails supporting the fireplace flue, with an air gap all around. So, if I were to use the fireplace, smoke would travel up the flue and the air gap! WTF! $&#@! I put some refractory cement on the end of a long stick and repeatedly plugged around the bottom of the clay liner. Hopefully it'd be enough to keep the clay liner anchored in place and the air gap blocked off. I also noticed that there was no parging on the smoke chamber walls. Arrrrgh. Also, the space between the brick veneer lintel and the metal damper seat was never sealed, possibly allowing hot gases up behind the veneer. More work.

I reached up and felt around behind the metal damper on the smoke shelf. #$@#$@! A giant mound of sand. Apparently the many years of no chimney cap had allowed water to wash decaying mortar....sand....onto the smoke shelf. Maybe it was the remains of non-refractory parging? I scooped out all of the sand. UGGGGH! A mummified bird!!!!!!! Another good reason to have a chimney cap!

Next stop, the roof. I see a square flue for the boiler and a rectangular flue for the fireplace. Ummmmmmm, why is there no wythe of brick between the two flues??? WTF?!!! #@$. Maybe that was the norm in 1965, but based on the crappy masonry I'd seen so far, probably not. I look down the fireplace flue. Hey good news, it all seems to be there and is reasonably aligned. Can't see any damage.

I look down the boiler flue. What on earth is that?!!! #$@#%!!!! The second to last piece of flue liner is missing. Had it broken and fallen out? Was it the one in the basment? No, no. Apparently the mason cheated. Realizing he was short a piece of flue liner, he decided to use a couple of concrete bricks turned on end to make up the height of the missing piece of liner. He then installed the last piece of liner on those, so that at first glance the top of the chimney looks fine. The concrete bricks are now very decayed lumps of pebbly sand. Man, if I could get my hands on the clown that built this!!!! More work.

So, where do I stand today? The fireplace flue now houses a metal woodstove flue inside the clay liners. However, based on what I've recently learned about NFPA 211 and UL 1777, that flue ought to be fully insulated. The boiler, which probably needs to be replaced in the next year or two, still vents as shown---which is far from ideal.

continued....
 

Attachments

  • [Hearth.com] Built better in the good old days of 1965? Hah! My scary chimney....long story.
    chimney1965.webp
    167.5 KB · Views: 658
Well, my options....
1. Have entire chimney torn down and rebuilt correctly (Two story house, outside chimney at end of house). I imagine that'd be very expensive.

2. Have both flues broken out (no wythe inbetween anyway) and have two air bladder/cast in place flues installed. What do they do in the gigantic ash dump? Break open the wall and install masonry divider and second cleanout access door?

3. Have insulated stainless liner installed on boiler flue when boiler is replaced in the next couple of years. Use cast-in-place insulation (Thermix etc.) around metal stove flue to upgrade it. How is the smoke chamber closed off when that insulation dropped down the around metal flue? Insulation jammed up around the pipe, with temporary supports?

4. Other recommendations to upgrade safety/performance at reasonable cost? Anyone with experience with DIY costs versus hiring someone for these options?
 
I favor option #2 because cast in place flues add strength and integrity to any chimney, especially yours. Easily do the 2 separate flues. I am not sure what they would do with the large ash area--fill it with the special insulated concrete mix I presume. I have a single 20' chimney with a new cast in place flue. However, I would not consider this a DIY project. Specialized equipment and 2 days and 2 workers to do my fairly straight forward job. Likely cheaper than the entire chimney rebuild (and that wouldn't be insulated or necessarily crack free). A couple stainless liners would be cheaper but do nothing to beef up/reinforce the inside of the brick chase/chimney. Your decision really rests on what you want to accomplish.
 