If effort to generate a hot issue debate here, place this one into I did not know category. Recent post advocated reducing the 6” requirement to 5.5” liners which only reduced the area from 28 sq “ to 23” not knowing the friction characteristics of corrugation, in effect they are telling that poster its ok to reduce it by 1/3 . The code is not the only source noting friction drag. The manufactures of the products themselves admit it. The testing labs have proven it. Many installers probably do not know it or ignore it and most who have corrugated liners do not want to hear about it from me This will be blast the messenger again. Then someone will point out, fuel collar reductions are common in Europe. The question of the day is, as an inspector, knowing other code prevent the reduction requirements of the exit fuel collar, How can I accept a 6” corrugated liner attached to a 6” flue collar?
Taken from the latest international Gas and Mechanical Codes
All fireplaces and wood heaters are classified as category I appliances. The Categories are determined by heat ranges
Chapter 5 : Chimneys and Vents
Section 504 Sizing of Category I Appliances Venting Systems
•Where a corrugated liner is used the maximum capacity is reduced 20%
•504.3.1.7 Liner System Sizing
Added reference to Table 504.3.5
We have a lot of post here where stoves with full liners do not draft correctly. How could they if their liner restricts draft 20%. Hopefully some installers will read this post and start sizing corrugated liners correctly.
This is one of the many questions. I will be asking all the building inspectors and state inspectors in attendance to my seminar in a couple weeks. I wonder what there reactions will be? Is a bad or un-enforceable code, meaning physical dimensions of existing 8” flues make it impossible to correctly line existing flues and forget if they are required insulation. It is impossible to get a 6.5” liner, which is what this, code says, is needed with ¾ insulation jacket? Who is right here? The inspector for failing every 6” corrugated liner? The installer, for installing them? The manufactures, for not disclosing the info or purposely hiding it? The code writers for not taking account real world field conditions? I’m leaving my opinion up till this issue is debated a while, but I have some solutions and suggestions
Taken from the latest international Gas and Mechanical Codes
All fireplaces and wood heaters are classified as category I appliances. The Categories are determined by heat ranges
Chapter 5 : Chimneys and Vents
Section 504 Sizing of Category I Appliances Venting Systems
•Where a corrugated liner is used the maximum capacity is reduced 20%
•504.3.1.7 Liner System Sizing
Added reference to Table 504.3.5
We have a lot of post here where stoves with full liners do not draft correctly. How could they if their liner restricts draft 20%. Hopefully some installers will read this post and start sizing corrugated liners correctly.
This is one of the many questions. I will be asking all the building inspectors and state inspectors in attendance to my seminar in a couple weeks. I wonder what there reactions will be? Is a bad or un-enforceable code, meaning physical dimensions of existing 8” flues make it impossible to correctly line existing flues and forget if they are required insulation. It is impossible to get a 6.5” liner, which is what this, code says, is needed with ¾ insulation jacket? Who is right here? The inspector for failing every 6” corrugated liner? The installer, for installing them? The manufactures, for not disclosing the info or purposely hiding it? The code writers for not taking account real world field conditions? I’m leaving my opinion up till this issue is debated a while, but I have some solutions and suggestions