Grundfos 26-99FC Was told this did not need to be the same size as the primary pump. I'am sure 1" copper and a small pump would work fine.
It is straightforward and should work as intended. But there is a gotcha if any of storage is above or at same level as boiler, in which case much of the cool water pumped into boiler will fall right back into bottom of storage unless there's a check valve.would be quite easy to install with a differential controller
One thing I like about the Froling that is innovative is that it cycles the loading unit after the burn is done and the boiler has otherwise shutdown to move to storage continued heat buildup in the Froling from the remaining hot coals. That heat otherwise likely would move up the stack and be wasted. A similar control on my Tarm may be an improvement for next summer and would be quite easy to install with a differential controller which would measure boiler hot water temperature and the temperature of the middle or near bottom of the tank.
A U-shaped heat trap also should prevent this from happening, wouldn't it?But there is a gotcha if any of storage is above or at same level as boiler, in which case much of the cool water pumped into boiler will fall right back into bottom of storage unless there's a check valve.
I think a trap would work if it goes up higher than the top of the boiler.A U-shaped heat trap also should prevent this from happening, wouldn't it?
I can't prove this, but I think it also kicks on the pump occasionally, just to exercise it. There have been a couple times in the summer, where the fire has been out for a couple days, amd I will hear the pump turn on for a few seconds, then shut off again...Yes, it will cycle intermittently for hours after burn shutoff. I have observed mine loading 130 degree water into the tanks almost 10 hours after the burn. A fact which in my system is more than welcomed and usable, I run my tanks down to 105 and auto switchover at 98. I am wondering if there is a condensation preventative strategy in the procedure, gauging the variation between vessel temp and flue gasses.
Also, how does the Fröling get water though/around the thermostatic valve when in scavenging mode?
I have the circ launch temp on the Froling set at 70 C which is just above the opening temp of the thermostatic loading unit. As described above, the boiler will shutdown, but remaining coals will relaunch the circs to scavenge heat with the boiler off and then go off again as soon as the boiler temp falls below the differential, about two degrees C. The circs wil cycle on and off for maybe three hours as the coals burn down with the boiler off. No scavenging below 69 C because the loading unit valve closes near there.
The factory setting for launching the circs was a few degrees lower and the loading unit was closed at that temp, making the oading unit circ run for hours around the boiler but no flow through the boiler with the loading unit valve closed. That's without the smart controls I have planned.
Pretty sure the circ launch parameter is just the boiler water temp setpoint, independent of the boiler firing or not.
I have seen scavenging and circ running below 69, I do not know what the setpont is in my controller is, I will chk and post, but I ahve definentely seen thew pump run in the low sixties.
Factory setting for release of pump at 149f(65C) and thermic element in LK Loading pump is also 149F.(as per LK cuts).
Do not know what the equation for triggering the mode, but I assume it is a relationship between Flue gas temp , Boiler Temp and Storage status(that one minimally, in this mode).
Here are some pix from tonight, boiler has been off since this morning's burn, LK loading pump was on when I checked(boiler was at 65C) and was running when boiler was down to 63C.
LK supply side was at 60-62C.
Top of Tanks were at 127F (50c).
System supply side was at 130(52.5c).
Right, the circ is running, but if the loading unit was open and allowing the cooler return water into the boiler (and removing the heat), the boiler would cool a lot faster with no fire. Supply temp at 52 C but the boiler is 65 C means the loading unit valve is closed and not allowing flow through the boiler. If the loading unit was open, it would only be ten or twenty minutes to cool the boiler below the circ launch temp and turn the circs off. The circ could be running but not moving heat with the valve closed. That's what I saw.
![[Hearth.com] DIY Fröling install [Hearth.com] DIY Fröling install](https://www.hearth.com/talk/data/attachments/120/120194-7f9fb25fce16d3879173f17d507e6593.jpg?hash=GW1vi__Zz4)