draft inducer

chuck172 Posted By chuck172, Aug 8, 2017 at 7:03 AM

  1. chuck172

    chuck172
    Minister of Fire 2.
    NULL
    

    Apr 24, 2008
    1,045
    5
    Loc:
    Sussex County, NJ
    Is anyone here using a draft inducer, such as a tjernlund on their basement wood boiler?
     
  2. hondaracer2oo4

    hondaracer2oo4
    Feeling the Heat 2.
    NULL
    

    Jan 18, 2012
    400
    59
    Loc:
    Canterbury NH
    I don't believe it is safe to rely on any type of mechanical draft inducer on a wood burning appliance. What happens if the the power goes out or the fan fails?
     
  3. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    8,108
    1,464
    Loc:
    Nova Scotia
    Depending what you have - it might come in handy at fire lighting time.

    Might also help in a marginal draft situation - but yes you would need to be cautious of what things would work like if it wasn't or stopped running when burning. Most, or many, of the good boilers have induction fans in them (so they are commonly relied on, so to speak).

    (No direct experience here...)
     
  4. chuck172

    chuck172
    Minister of Fire 2.
    NULL
    

    Apr 24, 2008
    1,045
    5
    Loc:
    Sussex County, NJ
    I would only use the inducer for starting and adding to the fire. I wouldn't rely on it. I once did have my boilers fan stop (fuse) smoke entered the basement. If I had the inducer installed, I could have prevented the smoke situation.
     
  5. hondaracer2oo4

    hondaracer2oo4
    Feeling the Heat 2.
    NULL
    

    Jan 18, 2012
    400
    59
    Loc:
    Canterbury NH
    Sounds like a good idea than for starting fires. My Heatmaster g200 has a smoke bypass door with inducer fan. I get zero smoke out of the door. Works awesome.
     
  6. goosegunner

    goosegunner
    Minister of Fire 2.
    NULL
    

    Oct 15, 2009
    1,461
    109
    Loc:
    WI
    Send me a pm with a email address and I will send you a video with my setup on a Econoburn. It is working extremely well.

    Basically it is a high cfm blower used to create a Venturi. The blower is on a switched outlet. Also on the outlet is a electro magnet that holds the barometric damper closed while blower is running.
     
  7. heaterman

    heaterman
    Minister of Fire 2.
    NULL
    

    Oct 16, 2007
    3,375
    629
    Loc:
    Falmouth, Michigan
    Sidewall venting you mean? That's a recipe for a disaster. Far as I know there is nothing on the market approved for wood.
    The difference is with an oil or gas burner the fuel can be cut off instantly if the draft inducer fails or power is lost.
    With wood, this is not possible.
     
  8. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    8,108
    1,464
    Loc:
    Nova Scotia
    I didn't think he meant sidewall or direct vent.
     
  9. chuck172

    chuck172
    Minister of Fire 2.
    NULL
    

    Apr 24, 2008
    1,045
    5
    Loc:
    Sussex County, NJ
    I do not mean sidewall venting.
     
  10. heaterman

    heaterman
    Minister of Fire 2.
    NULL
    

    Oct 16, 2007
    3,375
    629
    Loc:
    Falmouth, Michigan
    What are you trying to do? Is the draft too low? What does it measure?
     
  11. chuck172

    chuck172
    Minister of Fire 2.
    NULL
    

    Apr 24, 2008
    1,045
    5
    Loc:
    Sussex County, NJ
    I have a masonry chimney with a neg draft. The only way to start a fire is to crack a basement window. It's just about impossible to add wood to an already started fire without smoke.
    .
     
  12. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    8,108
    1,464
    Loc:
    Nova Scotia
    Sounds like some deeper issues that might need attention - and a condition that could be putting CO into your living space.

    My boiler is natural draft, and an inducer fan was suggested at the outset as a possibility if I had trouble getting my draft going on a cold startup. But turned out to not be an issue. I have 30' of 7" SS insulated flu though. I also keep a basement window that's right behind my boiler slightly cracked open all winter, with a piece of FG insulation stuffed into the crack.
     
  13. heaterman

    heaterman
    Minister of Fire 2.
    NULL
    

    Oct 16, 2007
    3,375
    629
    Loc:
    Falmouth, Michigan
    I agree with Maple. Combustion air or makeup air is lacking.
     
  14. jebatty

    jebatty
    Minister of Fire 2.
    NULL
    

    Jan 1, 2008
    5,561
    809
    Loc:
    Northern MN
    One of several brainstorm improvements to my Tarm was adding the automatic window opening to provide makeup air whenever the Tarm is operating. Makeup Air
     
  15. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    8,108
    1,464
    Loc:
    Nova Scotia
    We can't see the whole chimney either - have been assuming it is built/installed to specs etc. too. And if it is an uninsulated masonry chimney, that could compound - although that usually makes the draft hard to get going and maintain, & not make a downdraft per se. Then there are things like nearby trees or whatever, and the combo of prevailing winds & different roof lines that can sometimes do weird things to draft also. First thing I would check out is the outdoors height & roof relationship - without knowing anything about it.

    An inducer might still be something to consider, but I don't think they are intended to correct a negative draft issue. Especially since it was said it is negative even with an already started fire - or, perhaps that wasn't quite worded right. I think even with a proper chimney draft in action, it is still quite possible and maybe even very likely to get some spillage out the door when the door is opened in certain fire conditions.
     
  16. chuck172

    chuck172
    Minister of Fire 2.
    NULL
    

    Apr 24, 2008
    1,045
    5
    Loc:
    Sussex County, NJ
    When starting a fire, I'll have neg. draft. If I crack open a basement window the draft turns positive. I do have a manometer installed. When the fire is going I'll have a pos. draft, but will get some spillage if I add wood. I'm refering to neg as downdraft..
    I thought an inducer was intended to correct a neg. draft issue.
     
  17. maple1

    maple1
    Minister of Fire 2.
    NULL
    

    Sep 15, 2011
    8,108
    1,464
    Loc:
    Nova Scotia
    My understanding is they are to improve an insufficient draft - not really to correct a negative. But I might be off on that understanding. I could see why though - if the power goes out or the fan quits for some reason, then your draft goes negative and you have CO entering the house. A very bad thing in the middle of the night. Or any time really. Seeing your draft go from - to + when a window is cracked seems to point to a makeup air issue, or too much outward ventilation from somewhere else - like an unbalanced ventilation system or exhaust fans running that don't have to.
     
  18. Bad LP

    Bad LP
    Minister of Fire 2.
    NULL
    

    Nov 28, 2014
    525
    155
    Loc:
    Northern Maine
    My System 2000 LP boiler already had a fresh air supply into the airbox and vented to the chimney.

    For my Tarm I will be cutting into that supply and adding a 24VDC powered damper that will open when the wood boiler is in operation. It will only drop air near the boiler and will not be directly piped to it. It's first fire in May after install didn't produce any issues but I had to repipe the LP boiler anyway so it was already disassembled.
     
  19. aaronk25

    aaronk25
    Member 2.
    NULL
    

    Feb 15, 2017
    113
    87
    Loc:
    Rochester
    Ya even with .07 inches of water column with my blaze king princess 6" chimney it's almost impossible to do a reload mid burn to "top it off" with out letting smoke out. The 6" chimney even with a lot of draft just doesn't create enough velocity to be able to keep all the smoke in the stove. I know the main reason for these smaller diameter chimneys are to run more efficient and keep the chimney temp up (even as little as it is now 250-300) but they suck at reloads


    Sent from my iPhone using Tapatalk
     
  20. Indianadave

    Indianadave
    New Member 2.
    NULL
    

    Dec 1, 2017
    4
    0
    Loc:
    Marion
    Something used on later steam locomotives with short smoke stacks, was called a blower. It simply was a steam line which was vented directly up into the stack which created the venturi effect to increase draught.
    A friend was having smoke issues when firing up his forge. I suggested introducing a small air line into the double wall chimney for the same effect. It works really well as, is doesn't take much air to induce a draught. He used a small compressor with a ball valve in line to adjust the flow. It just has to be introduced into the last vertical section of the chimney somewhere.
     
  21. Indianadave

    Indianadave
    New Member 2.
    NULL
    

    Dec 1, 2017
    4
    0
    Loc:
    Marion
    I guess I didn't mean the VERY last SECTION of vertical chimney pipe. Just somewhere in the vertical part of the chimney.
     
  22. HappyHome

    HappyHome
    New Member 2.
    NULL
    

    Jan 7, 2017
    8
    0
    Loc:
    Ottawa, ON
    Hello.

    I have had several problems with smoke escaping into the roomduring startup and loading. I’d like to seeyour draft inducer setup qs well, if you don’t mind.

    I have an econoburn 100, that i’m still figuring out.

     
  23. goosegunner

    goosegunner
    Minister of Fire 2.
    NULL
    

    Oct 15, 2009
    1,461
    109
    Loc:
    WI
    Here are some pictures. I have since sold the Econoburn and am now running a Froling S3 which is simply amazing!!.

    The Exhaust pipe extended up the inside of the flue through the bottom of a T to maybe 8" past the flue outlet of the boiler.

    The blower was on a switched outlet along with a electro magnet that would keep the barometric damper closed when the switch was on and the blower was running.

    ****IMPORTANT POINT*** The blower was only used when lighting or reloading the boiler. I virtually eliminated the smoke escape during those times. I have a good video but it is too large to load here.

    Blower1.JPG Blower2.JPG Blower3.JPG
     
  24. NP ALASKA

    NP ALASKA
    Burning Hunk 2.
    NULL
    

    Feb 3, 2008
    232
    44
    Loc:
    North Pole, ALASKA
    Try changing your chimney cap. We changed ours to a directional cap that spins with the wind. You can find them on the internet. The lack of pressure at the end of the pipe inceeased velocity and we now have been loading the BK Princess with no more smoke issues.
    Just a thought
     
    aaronk25 likes this.
  25. NP ALASKA

    NP ALASKA
    Burning Hunk 2.
    NULL
    

    Feb 3, 2008
    232
    44
    Loc:
    North Pole, ALASKA
    http://www.firewood-for-life.com/chimney-cowl.html

    Like this
     