Hi there! I’ve been reading some old posts by mpoyneer on modifying his Econoburn boiler. I just recently installed a brand new (in 2008) econoburn 150 that hasn’t ever had a fire in it until this last Saturday. I am interested to know if the modification to stop the draft fan from running after the fire went out worked well in the long run. I see where he used a relay and a bypass switch to solve this issue. I copied the post below:
"cooling Fan" problem solved!
Omron LY2-AC110/120 DPDT relay wired in the power supply to the Nimbus (terminals "N" and "L")
- opens circuit on the alarm 1 setpoint via terminals 9 and 10 on the TC33 controller
- You have to make sure the Function for alarm 1 is set to "Low Alarm" by setting "A1Fu" to "0"
- pump must be wired directly to power and not controlled by the boiler controls
Just would like to know if this worked well in the long run. Is there a way to contact this member?
Thanks,
Roy
"cooling Fan" problem solved!
Omron LY2-AC110/120 DPDT relay wired in the power supply to the Nimbus (terminals "N" and "L")
- opens circuit on the alarm 1 setpoint via terminals 9 and 10 on the TC33 controller
- You have to make sure the Function for alarm 1 is set to "Low Alarm" by setting "A1Fu" to "0"
- pump must be wired directly to power and not controlled by the boiler controls
Just would like to know if this worked well in the long run. Is there a way to contact this member?
Thanks,
Roy