Mike, a few more questions about the 17-VL:
1. Why does your company find it necessary to sell this model under 3 different brand names?
the line names were created to allow a larger market share by selling to different stores in the same areas
2. Are any rear or side heat shields available for it?
no, there is not heat shield setup for this model
3. I looked in its manual but did not see any guidance about reducing rear CTC with a wall heat shield. Is this approved?
the reason there is no allowance for additional clearance reduction is the unit already is allowed a tighter clearance as it sits than is allowed by the NFPA211 reductions chart ( table 12.6.2.1) which allows only a reduction of a percentage OR a minimum clearance defined by the type of protector for instance a 1/2 inch millboard with 1 inch ventilated air space in the 211 allows for a reduction of 66% OR reduction to 12 inches whichever is GREATEST of the two.
now since the 17-vl is already listed to be placed at 12 inches or less without adding wall protection you already are as close as you are allowed by the 211 to start out.
4. I'm not aware of any other Washington certified stove that costs less - are you? If not, what compromises did you make to achieve your price point? Safety, durability, reliability, ease of use, etc?
i wouldnt know of any less expensive Wash. state certified units that may be out there. as for compromises to hold a lower price point , the biggest thing is the elimination of the "dealer" service type of warranty. also the sheer numbers of stoves we produce and sell allows for smaller margins per stove.
its not really a compromise its just the way our buisness model is set up
5. Have you ever heard of anyone combining your least expensive stove with the most expensive chimney, which I am guessing would be ICC Excel?
what compromises did you make to achieve your price point? Safety, durability, reliability, ease of use, etc?
Yeah Mike, where are the compromises? I have been looking for them on my 30-NC since 2006. Ya must have hidden them well.
the 17-vl is already listed to be placed at 12 inches or less
How much less?
10" single wall pipe, 8" double wall: http://www.englanderstoves.com/manuals/17-VL.pdf (page 7)
That far away from the stove the measurements are to the pipe. Single wall connector pipe requires 18" clearance to the wall. Double wall requires 6" to the wall.
It is from anything that can burn.