I put a fireplace in my house. Put the install up for a inspection to ensure insurance coverage, and wouldnt you know the inspector has picked something to fail the install on, the lack of a intake vent. The inspector and supervisor of the department of planning tried nailing me on one of their Snohomish County regulations listed under their amended IRC Codes,
"SOLID FUEL BURNING APPLIANCES AND FIREPLACES: Solid fuel burning appliances and fireplaces shall satisfy one of the following criteria.
402.2 Solid Fuel Burning Appliances: Solid fuel burning appliances shall be provided with the following:
a. Tight fitting metal or ceramic glass doors.
b. 1. A source from outside the structure of primary combustion air, connected to the appliance as per manufacturer’s specification. The air inlet shall originate at a point below the fire box. The duct shall be 4 inches or greater in diameter, not exceed 20 feet in length, and be installed as per manufacturer’s instructions;
or
2. The appliance and manufacturer’s recommended combustion air supply, as an installed unit, shall be certified by an independent testing laboratory to have passed Test No. 11-Negative Pressure Test, Section 12.3, of ULC S627-M1984 “Space Heaters "
I was able to convince them that this would work because of option#2 which my stove is certified ULCS627.
Now thet are attempting to attack my manufacturers requirements:
I have a Napoleon 1100 built in 2000. The manual states that a intake vent is only req for a mobile home, but on the introduction page listing a plethora of warning it states this, "- At least 14 square inches of outside air must be admitted to the room or directly to the unit through a 4” diameter pipe"
Now what the hell does this mean? Anyone? Im calling the manufacturer in the AM but this has me all flustered. and though id ask on this forum, thanks.
"SOLID FUEL BURNING APPLIANCES AND FIREPLACES: Solid fuel burning appliances and fireplaces shall satisfy one of the following criteria.
402.2 Solid Fuel Burning Appliances: Solid fuel burning appliances shall be provided with the following:
a. Tight fitting metal or ceramic glass doors.
b. 1. A source from outside the structure of primary combustion air, connected to the appliance as per manufacturer’s specification. The air inlet shall originate at a point below the fire box. The duct shall be 4 inches or greater in diameter, not exceed 20 feet in length, and be installed as per manufacturer’s instructions;
or
2. The appliance and manufacturer’s recommended combustion air supply, as an installed unit, shall be certified by an independent testing laboratory to have passed Test No. 11-Negative Pressure Test, Section 12.3, of ULC S627-M1984 “Space Heaters "
I was able to convince them that this would work because of option#2 which my stove is certified ULCS627.
Now thet are attempting to attack my manufacturers requirements:
I have a Napoleon 1100 built in 2000. The manual states that a intake vent is only req for a mobile home, but on the introduction page listing a plethora of warning it states this, "- At least 14 square inches of outside air must be admitted to the room or directly to the unit through a 4” diameter pipe"
Now what the hell does this mean? Anyone? Im calling the manufacturer in the AM but this has me all flustered. and though id ask on this forum, thanks.