I appreciate all of the assistance I have gotten from you all so far. Before I fire it up I would like an internet inspection. Tell me what you think.
Highbeam said:To gain clearance from that roof rafter you need to move the whole chimney away from it. Yes, that means your ceiling cutout is in the wrong place. The ceiling support box needs to be moved 1" in the direction which will provide more clearance to that rafter. Good thing you cut the roof decking out to 3" instead of 2", you'll need that extra inch.
Don't be tempted to lean your chimney. It'll look silly.
RocketMan said:You are not ready to light a fire yet! The roof clearance to the pipe should be a minimum of 2" all the way around. The 6 to 8 adapter should be inserted into the stove flue, not on the outside (creosote flow). I think the framing for the ceiling support box should also have some clearance, framed for the size of your attic insulation shield. Be safe!