I have a Froling 20 which was up and running at the end of January 2015. I had the same message and after a number door adjustments the messages continued for about every 1 of 2 burns. I contacted the boiler rep who provided the sequence which generates the message, it is as follows.
The Boiler has a timer “SAFETY time for checking for air leaks” this timer is initiated when the outer door is closed and the secondary air actuator is at 0% open and the flue gas temperature is over 100°C (212°F). If these conditions are true and the time expires the message is generated. The boiler is shipped with a value of 90 minutes.
At the end of the burn when the fire is going out, secondary air is not needed when there is a bed of coals and the flue temperature is over 100°C. A couple of ways to stop the message
- If you open and close the outer door near the end of the burn you will reset the timer sequence
- The easiest solution is to length the timer