I received error 02 "Primary Air Damper Blocked" a couple of times over the last couple days. Any Froling users experience this?
I'll post the page from the manual on the trouble shooting section but, essentially it can be from a bad cable, miscommunication or position mismatch >5%.
I verified no damage to the cable and good plug connection. Also verified no physical blockage or excessive restriction to the damper.
I went into service mode to Analog Outputs and told the primary damper to move to 0% (closed) and the damper will not close more than 40%. I input a demand of like 35% and it moves to 45%... I demand 100% and it will move open but stops at about 58%. Demand 0% and it won't go lower than 40%.
I tried the same thing with the secondary and it goes to whatever I tell it to.
I think this points towards the positioner malfunction but unsure how else to troubleshoot these. Any input is appreciated.
I'll post the page from the manual on the trouble shooting section but, essentially it can be from a bad cable, miscommunication or position mismatch >5%.
I verified no damage to the cable and good plug connection. Also verified no physical blockage or excessive restriction to the damper.
I went into service mode to Analog Outputs and told the primary damper to move to 0% (closed) and the damper will not close more than 40%. I input a demand of like 35% and it moves to 45%... I demand 100% and it will move open but stops at about 58%. Demand 0% and it won't go lower than 40%.
I tried the same thing with the secondary and it goes to whatever I tell it to.
I think this points towards the positioner malfunction but unsure how else to troubleshoot these. Any input is appreciated.