I've noticed several posts stating, if I remember correctly, that firing to maintain a lower (165F+/-) boiler supply temp, if it satisfies demand, is more efficient that firing which results in a higher boiler supply temp. I don't recall whether or not these systems had storage.
After 2 days of experimenting with a new control system, which resulted in changing when I start the circulator after firing the Tarm, I noticed that:
1) Prior use started a low speed circ shortly after firing to recirculate boiler water and then start supply to the system when boiler supply reached 160F. Early burn recirculation meant that the entire boiler water content (about 54 gal with the Tarm) would also be close to 160F. With the boiler in high burn, return water from system at 120F or so, boiler would max out at about 170F supply until return started to rise, and then boiler supply also would rise. Probe flue temp 500-600F.
2) The experiment was to fire the Tarm to achieve boiler supply temp of 185F before starting the circ. With the boiler in high burn, return water from system at 120F or so, the boiler would hold a consistent supply of 183-190F (my circ setup increases flow at 185F and above), even as return rose from 120F to almost 170F. At that point I allowed the wood load to finally burn down, no boiler idling occurred, and 1000 gal storage ended up at 186F top to bottom. Probe flue temp 500-600F, same as before. This experiment was not intentional, but was accidental and was related to configuring a different control setup.
3) I did not weigh the amount of wood burned during either burn.
What is the conclusion? Since probe flue temp was the same during both burn periods, it would seem that burn efficiency was about the same in both cases. The experimental burn, however, resulted in much higher btu output. I can't calculate the increase exactly, as my flows change with boiler supply temp, but I was maintaining a 13-20F increase in supply temp over prior experience, and flow rates also were at least 4 gpm higher when supply was over 185F than when supply was 170F.
The increase in btu output must have resulted from a faster rate of burn, thus producing more btu's, and from extraction of those extra btu's to heated water, as probe flue temp was the same in both cases.
It would seem, therefore, that burn heat extraction to water efficiency increased during the experimental burn. This efficiency must be related to the firebox being surrounded by water at 183-190F vs 160-170F. A gassifer, at least the Tarm, does have water around most of the firebox.
From the experiment I would conclude that, if a system has a means to use the extra btu output, storage for example, maintaining a hotter supply temp will result in more btu output and faster storage charging without a decrease in burn efficiency, and therefore will result in shorter burn time, although more frequent loading of wood will be required during the burn cycle.
I have harbored a mild disappointment in that I was not able to achieve consistent btu output close to the 140,000 btu rating of the Tarm, except at very high delta-T's. This experiment indicates that the Tarm in fact probably can produce consistently high btu output approaching its btu rating by using the experimental burn procedure.
I would have to regard this report as somewhat anecdotal, as I did not keep accurate data during the burns, but I do pay quite close attention to operation of the Tarm, I have temperature measurements at a number of locations, I have a flowmeter in the system, and I believe that what I have related would be substantially supported by data. My confidence is such that I likely will continue this burn procedure.
After 2 days of experimenting with a new control system, which resulted in changing when I start the circulator after firing the Tarm, I noticed that:
1) Prior use started a low speed circ shortly after firing to recirculate boiler water and then start supply to the system when boiler supply reached 160F. Early burn recirculation meant that the entire boiler water content (about 54 gal with the Tarm) would also be close to 160F. With the boiler in high burn, return water from system at 120F or so, boiler would max out at about 170F supply until return started to rise, and then boiler supply also would rise. Probe flue temp 500-600F.
2) The experiment was to fire the Tarm to achieve boiler supply temp of 185F before starting the circ. With the boiler in high burn, return water from system at 120F or so, the boiler would hold a consistent supply of 183-190F (my circ setup increases flow at 185F and above), even as return rose from 120F to almost 170F. At that point I allowed the wood load to finally burn down, no boiler idling occurred, and 1000 gal storage ended up at 186F top to bottom. Probe flue temp 500-600F, same as before. This experiment was not intentional, but was accidental and was related to configuring a different control setup.
3) I did not weigh the amount of wood burned during either burn.
What is the conclusion? Since probe flue temp was the same during both burn periods, it would seem that burn efficiency was about the same in both cases. The experimental burn, however, resulted in much higher btu output. I can't calculate the increase exactly, as my flows change with boiler supply temp, but I was maintaining a 13-20F increase in supply temp over prior experience, and flow rates also were at least 4 gpm higher when supply was over 185F than when supply was 170F.
The increase in btu output must have resulted from a faster rate of burn, thus producing more btu's, and from extraction of those extra btu's to heated water, as probe flue temp was the same in both cases.
It would seem, therefore, that burn heat extraction to water efficiency increased during the experimental burn. This efficiency must be related to the firebox being surrounded by water at 183-190F vs 160-170F. A gassifer, at least the Tarm, does have water around most of the firebox.
From the experiment I would conclude that, if a system has a means to use the extra btu output, storage for example, maintaining a hotter supply temp will result in more btu output and faster storage charging without a decrease in burn efficiency, and therefore will result in shorter burn time, although more frequent loading of wood will be required during the burn cycle.
I have harbored a mild disappointment in that I was not able to achieve consistent btu output close to the 140,000 btu rating of the Tarm, except at very high delta-T's. This experiment indicates that the Tarm in fact probably can produce consistently high btu output approaching its btu rating by using the experimental burn procedure.
I would have to regard this report as somewhat anecdotal, as I did not keep accurate data during the burns, but I do pay quite close attention to operation of the Tarm, I have temperature measurements at a number of locations, I have a flowmeter in the system, and I believe that what I have related would be substantially supported by data. My confidence is such that I likely will continue this burn procedure.