Harman insert exhaust concerns

mbroughton02 Posted By mbroughton02, Dec 2, 2017 at 6:44 PM

  1. mbroughton02

    mbroughton02
    New Member 2.
    NULL
    

    Oct 30, 2017
    11
    2
    Loc:
    Cortland, NY
    Brand new Harman Accentra 52i seems to be burning dirty. I completely cleaned the stove last weekend, and again yesterday. This is what it looked like yesterday, after only 5 bags of pellets:

    Ash is very clumpy
    Ivb2uLRl.jpg

    GsuiVLdl.jpg

    XaRnFWil.jpg

    Lots of black ash or soot on the door
    nQK3PY3l.jpg

    The stove was installed by a Harman dealer. I noticed visible smoke from the chimney today so I decided to go up and see what they did up there. I have an outside air kit which they ran all the way to the top, as well as the exhaust.

    I'm thinking I may have found some problems:
    1) The exhaust fitting is a 3" fitting, which means there is a restriction at the end of the 25' long 4" stainless steel liner.
    2) The fitting terminates only about 1" below the slate chimney cap, further restricting the exhaust.
    3) The outside air liner was run all the way to this cap as well, but due to the slate chimney cap, the air that it's sucking in likely contains a lot of exhaust.

    Hi561tTl.jpg

    llUwDutl.jpg

    yOQf9dvl.jpg

    EOSTXZZl.jpg

    Thoughts?
     
  2. mikkeeh

    mikkeeh
    Feeling the Heat 2.
    NULL
    

    Dec 7, 2011
    263
    56
    Loc:
    NE Ohio
    If I understand correctly its a 4” flue, restricted to a 3” termination?? Yea, that doesn’t make sense. And I would agree that the fresh air intake is way too close to the exhaust. I think you’re on the right track. Unfortunately, it doesn’t always pay to have professionals do the install. Keep us posted on what you find.
     
  3. mbroughton02

    mbroughton02
    New Member 2.
    NULL
    

    Oct 30, 2017
    11
    2
    Loc:
    Cortland, NY
    Yeah, I'm a big DIY guy. But New York offered a $1,500 rebate on the pellet stove for trading in a wood stove. One of the requirements was professional installation from a dealer on their list, so I had no choice unless I wanted to give up the rebate. But I would much rather have done the install myself.
     
  4. mikkeeh

    mikkeeh
    Feeling the Heat 2.
    NULL
    

    Dec 7, 2011
    263
    56
    Loc:
    NE Ohio
    I hear ya. Many times you find the “professionals “ don’t know as much as you do. If it were me, I’d loose the 3” termination fitting and extend 4”pipe through the cap a couple of feet. Then a 4” weather cap on top of that. That way your current chimney cap protects the fresh air intake. JMHO
     
    bags and alternativeheat like this.
  5. alternativeheat

    alternativeheat
    Minister of Fire 2.
    NULL
    

    Dec 19, 2013
    3,667
    1,191
    Loc:
    Cape Cod, Ma.
    I really don't think it's going to make a whole lot of difference if you terminate with 3 or 4 inch, the main run is 4. It would make even less sense if the run was 3 and the termination 4, by that point it's too late. For the sake of fit though I'd possible use 4 inch, and did on my own 35 ft run up the chimney.

    However, if that intake is in line with the outlet, that's bad. I only ran 7 ft up my chimney with the OAK, so effectively have more than 25ft separation. Your OAK tube generally doesn't run to the top, there is restriction if too long, same as the vent restricts if too long, too twisted up etc. I think Harman allows a 10 ft run but in my case I also use 3" OAK tube. This stove breaths awesome too. It's ash is basically powder and it burns any pellet.
     
    bags likes this.
  6. JRemington

    JRemington
    Member 2.
    NULL
    

    Nov 4, 2017
    165
    32
    Loc:
    Belleville New York
    Swing the insert out and unhook the air intake and see if that makes a difference. It looks like a combustion air problem. Did they set the draft? We are in NY and also do the NYSERDA rebate. The rules say the STOVE has to be installed and inspected by a certified pellet technician.
     
  7. rickwai

    rickwai
    Feeling the Heat 2.
    NULL
    

    Nov 1, 2011
    436
    85
    Loc:
    ohio
    I agree with JREM. Unhook air intake to rule it out. Then if that dont help get a couple bags of different pellets. We had some pellets in our area a few years back that burnt like that
     
    bags and bogieb like this.
  8. fastrac

    fastrac
    Member 2.
    NULL
    

    Sep 28, 2006
    48
    0
    Good diagnostics on your part, Clean it, run it with out the slate and see how it burns .

    You have correctly diagnosed the problem , Not you just have to get a new termination set up
     
  9. mbroughton02

    mbroughton02
    New Member 2.
    NULL
    

    Oct 30, 2017
    11
    2
    Loc:
    Cortland, NY
    I took off the slate cap last night and let the stove burn for about 12 hours. Unfortunately it didn't make much difference. The glass was still pretty dirty and I got a cup of clumpy ash from 1/2 bag of pellets. So this morning I unhooked both the exhaust and intake from the stove so that I could get a better look at what's under the cap:

    D234z9Ll.jpg

    You can see that the exhaust is pretty restricted, going from a 4" down to a male 3" fitting. So for today I am leaving this chimney cap apparatus off completely. I reconnected both pipes to the stove and its burning now. I will let it go for 8-10 hours but will need to put the chimney cap back together before the end of the day, because right now rain and critters can just go right down the flue or liners.

    No, they did not test the draft with a magnehelic or do any draft voltage adjustment.

    I have tried a few bags of at least 5 different brands of pellets, including Lignetics. The pellets I'm using currently are Barefoot. I tried several others as well. None were better, but some were worse.
     

    Attached Files:

    rickwai likes this.
  10. Cody901

    Cody901
    New Member 2.
    NULL
    

    Oct 19, 2016
    49
    4
    Loc:
    Maryland
    I’ve installed two of these stoves in the past year. The first stove I installed in my old house I made the terminations similar to your set up but I added a piece of metal in between the intake and exhaust and never had any issues. In my new house I terminated the intake in the chimney and used harmans chimney top cap and have had no issues with this setup either. I will attach acouple photos of the two setups. I would suggest the harman chimney cap and just cut your oak as far down as you can reach.
    7bfd568a0d2d35acdc75267d5254f505.jpg 85714a4e343543ad73c43d45d9ef3e4e.jpg eecf229d3b49d42ebab2c40ae75dbfb6.jpg


    Sent from my iPhone using Tapatalk
     
  11. JRemington

    JRemington
    Member 2.
    NULL
    

    Nov 4, 2017
    165
    32
    Loc:
    Belleville New York
    Actually the 3 to 4 is standard for a liner. You need to unhook the air intake and see if it makes a difference. You have a combustion air problem.
     
  12. rickwai

    rickwai
    Feeling the Heat 2.
    NULL
    

    Nov 1, 2011
    436
    85
    Loc:
    ohio
    When you have the stove out make sure the flapper is not sticking on the air intake. I have seen this happen once on a brand new unit. It took us 1/2 of a season to figure out what was wrong with that stove!
     
    bags likes this.
  13. mbroughton02

    mbroughton02
    New Member 2.
    NULL
    

    Oct 30, 2017
    11
    2
    Loc:
    Cortland, NY
    Thanks for the tip. I checked the flapper today. It was moving freely. Outside air liner has been completely disconnected from the stove as of this evening. The stove wasn't burning any better today with no chimney cap, so this is the next step. We'll see how it goes tonight/tomorrow...
     
    rickwai likes this.
  14. mbroughton02

    mbroughton02
    New Member 2.
    NULL
    

    Oct 30, 2017
    11
    2
    Loc:
    Cortland, NY
    Ok so even with the outside air liner completely disconnected from the stove (so the stove is free to suck in room air), I'm still getting a dirty burn. I bought a magnehelic gauge on ebay which came in today.

    Cold stove readings with OAK liner disconnected but exhaust connected:
    Combustion blower @ full voltage = -.4
    Combustion blower @ "max" factory setting 2,900 RPM = -.37 (Harman install manual calls for -.45 to -.50)
    Combustion blower @ "min" 2,500 RPM = -.28 (Harman install manual calls for -.20 to -.26)

    So clearly I am not getting adequate draft. After taking these readings I disconnected the exhaust from the stove and tried again. The readings did not change. There must be something wrong with the stove itself. Emailing the dealer now...
     
  15. JRemington

    JRemington
    Member 2.
    NULL
    

    Nov 4, 2017
    165
    32
    Loc:
    Belleville New York
    What was the WCI pressure in the firebox?
     
  16. bob bare

    bob bare
    Minister of Fire 2.
    NULL
    

    Oct 31, 2013
    2,035
    352
    Loc:
    park county montana
    Well,unless Harman did some upgrade I am not aware of,your stove has the wrong impeller on the combustion blower.
     
    Ssyko likes this.
  17. mbroughton02

    mbroughton02
    New Member 2.
    NULL
    

    Oct 30, 2017
    11
    2
    Loc:
    Cortland, NY
    Fascinating, someone on the "Pellet Stoves" facebook group put out that possibility.

    What I have:

    ewscotNl.jpg

    What the parts diagram in my owners manual says I should have:

    Ev8SPqsl.jpg

    Very interesting...
     
  18. rickwai

    rickwai
    Feeling the Heat 2.
    NULL
    

    Nov 1, 2011
    436
    85
    Loc:
    ohio
    The 52i test port is tee'd into vac hose I think. There is no port in firebox like the original Acccentra

    Harman did change the fan and motor. I think it is a threaded motor shaft and fan blade instead of the set screw type. The look of the new fan reminds me of the Quad fans. I have not seen one in person yet.
     
  19. bob bare

    bob bare
    Minister of Fire 2.
    NULL
    

    Oct 31, 2013
    2,035
    352
    Loc:
    park county montana
    That shaft is not threaded,so I would assume he has a leftover 52i,not a touch control 52i,which means the impeller is wrong.Dealer probably needed it for a repair,then threw the quad impeller on there,thinking it would be OK.Yes,all the touch control harmans have an ebm/papst style motor.
     
  20. mbroughton02

    mbroughton02
    New Member 2.
    NULL
    

    Oct 30, 2017
    11
    2
    Loc:
    Cortland, NY
    This is a touch control 52i. Although the manual for the touch control version claims that draft is checked by removing a bolt in the lower left of the firebox, and there is no such bolt on this unit. Instead it has a piece of silcone hose sticking out near where the power cord connects behind the left panel, as @rickwai described. You're making me wonder if my unit was assembled using parts from several others...
     
  21. bob bare

    bob bare
    Minister of Fire 2.
    NULL
    

    Oct 31, 2013
    2,035
    352
    Loc:
    park county montana
    If dealer seems reluctant to help,call Harman.
     
  22. bob bare

    bob bare
    Minister of Fire 2.
    NULL
    

    Oct 31, 2013
    2,035
    352
    Loc:
    park county montana
    I blew up your picture,ya looks like a nut on fan, my mistake,There is a Harmon trained tech that can help,but was booted from here,he is on another forum.
     