surf_n_bid

New Member
Mar 3, 2014
2
east coast
finished a install with a monessen direct vent and noticed some discrepancies in the owner/ install manual or maybe its me... the manual states rough opening of "41.75 inches height" and "do not use flanges for framing or header" , "for drywall support only" BUT my header is at the flange? any input or suggestions appreciated? i really don't want to start cutting up the framing...
(broken image removed)
screenshot software for windows

(broken image removed)
 
Definitely contradictory. If you're worried about the location of the header, replace it with a steel stud.
If you've met the specifications for the rouch opening, I wouldn't worry about it, tho.
I've installed hundreds of gas ZC boxes & screwed EVERYONE of them to the header...
 