Here is a system I have been trying this summer. With 5 collectors in a drainback I can keep about 150 gallons of my system around 160- 170 in the summer, easily. In the winter it will be heated by solar and wood. So far I have not need to supplement the DHW this system produces.
Basically when any hot water faucet is turned on a Sika flow switch turns on a small circ to circulate the DB water thru the A side of the HX. The cold well water flows thru the other side and is heated instantly. It takes about 5 seconds to get up to temperature after the faucet is opened.
The next Caleffi I-dronics 11 will be on DHW, here is a preview of some of the concepts.
The 5X12- 30 HX is exactly what I used on mine and it supplies 3 GPM non stop, easily.
The main goal it to not have to store DHW, and eliminate the possibility of Legionella potential in a DHW tank that falls below 120F.
There are codes in Europe that regulate DHW production. Most folks have tankless. If a tank style DHW is used, it must be elevated every 24 hours to 60C (140F) for 60 minutes.
I notice more and more of these pre-plumber DHW heat exchanger systems arriving over here. Viessmann offers a nicely packaged instant DHW HX box to be added to their boilers.
The solar drawing credit: Appropriate Design
hr
Basically when any hot water faucet is turned on a Sika flow switch turns on a small circ to circulate the DB water thru the A side of the HX. The cold well water flows thru the other side and is heated instantly. It takes about 5 seconds to get up to temperature after the faucet is opened.
The next Caleffi I-dronics 11 will be on DHW, here is a preview of some of the concepts.
The 5X12- 30 HX is exactly what I used on mine and it supplies 3 GPM non stop, easily.
The main goal it to not have to store DHW, and eliminate the possibility of Legionella potential in a DHW tank that falls below 120F.
There are codes in Europe that regulate DHW production. Most folks have tankless. If a tank style DHW is used, it must be elevated every 24 hours to 60C (140F) for 60 minutes.
I notice more and more of these pre-plumber DHW heat exchanger systems arriving over here. Viessmann offers a nicely packaged instant DHW HX box to be added to their boilers.
The solar drawing credit: Appropriate Design
hr
(if any) to avoid legionella would need to come from wood or another source. The caleffi Idronics has provided to be excellent sources of information and piping arrangements. I look forward to reading and studying it when it comes out.