I am in the process of measuring the inside of my fireplace and I just wanted to make sure this is just a bent 6" liner and not ovalized. Here are some pics if anyone can help me out.
It actually looks like the damper was removed which makes me think they may have smashed the whole thing. Also that is not the correct adapter for lightwall liner on the bottom. It should have a band clamp not screws.What would you recommend to do? Flashing my light up there it looks like you are right about it being smashed probably from the damper. I can't see the damper though to tell whether or not it was removed.
I dont know what clearances do you have from the outside of the chimney structure to any combustibles? Is the liner insulated? Have you had the liner scanned to see if any of those kinks caused a hole? Is the new stove manufacturer ok with downsizing from 6"?As long as my liner is still intact which I believe it is, is it okay to re use this for a new insert?
No if it is an internal chimney you need 2" between the outside of that brick and any combustible material unless the liner is insulated.The chimney is an internal chimney so depending on how close the liner is to the bricks, the bricks are 4" thick so at least 4". I have no idea about if the liner is insulated I would say probably not being that they smashed the damn thing. I haven't had the liner scanned, I paid a chimney sweep to clean it and thought he would investigate the liner some , but all the 170$ got me was 30 minutes of cleaning from the bottom. Planning on a blaze king insert as far as the stove.
Ok then disregard my last post.The ones I'm looking at are only 6" since they are the Inserts. I'll talk to these guys tomorrow about it, thanks for the help I appreciate it.
Yes the liner is probably not insulated and it really should beBholler as far as seeing if it was insulated there should be another layer, or wrap correct? The inside of the pipe is just as rigid as the outside, so id say It isn't insulated. And since it's in the center I know studs/ joists and framing is definitely right next to the chimney. Burning it with my current stove last winter not knowing it might not be safe, the brick would get fairly warm if I was able to burn 24/7 for a few days
You will probably not have enough room for pour in. You need 1" on all sides of the liner. Which if they ovalized like that you wont have room.Thanks for the help guys. If it's okay maybe I can have someone pour vermiculite down it to insulate it.
Your options to bring it up to code are
1 pull that liner and replace it with a properly sized and professionally ovalized liner wrapped in insulation.
2 Remove the stainless and old clay liners and install a new 6" round liner.
3 pull the stainless and replace it with preinsulated dura liner if the chimney is straight enough for it.
Yes but what size is the clay linerYeah it surprises me that they struggled to get it down because my chimney is massive. I'd have to measure it but I'd say 3 foot wide by 4 foot long at least running from the basement all the way about 4 feet past the roof. I do have 1 other flue in it, a clay liner for the gas water heater
Without being onsite i cant say which is a better optionAs far as #3 after the smoke shelf there the little bend you see in the pics it goes straight up all the way. I will have to go the safest and affordable route, which the wife will kill me that we need a new flue, but we need to be safe no questions asked and I don't want to give up burning wood!