I see. We have a good bit of space between the stove and the throat/where the old damper was... would using a reducer be viable instead of needing to install a damper all the way at the top of the chimney? Given this is 42'... all work up there requires lifts, lifts are expensive, etc etc.

So we could do something like 5.5" ss flex liner => 4" reducer => back to 5.5" to connect to stove. If my math is correct a 4" reducer would cut airflow by like 50%? 4.5" is -35%. 5" is -18%.
 

bholler

Chimney sweep
Staff member
Jan 14, 2014
31,980
central pa
I see. We have a good bit of space between the stove and the throat/where the old damper was... would using a reducer be viable instead of needing to install a damper all the way at the top of the chimney? Given this is 42'... all work up there requires lifts, lifts are expensive, etc etc.

So we could do something like 5.5" ss flex liner => 4" reducer => back to 5.5" to connect to stove. If my math is correct a 4" reducer would cut airflow by like 50%? 4.5" is -35%. 5" is -18%.
Not a damper at the top of the chimney a key damper probably 2 in your case right above the stove
 

north-east-colonial

New Member
Dec 9, 2022
27
North East, USA
Ah I see. Just found some other threads, e.g. https://www.hearth.com/talk/threads/insert-key-damper-install.186463/

So it looks like a few things need to be decided:

1) Do it in the collar? Or the pipe? And if the better answer is the pipe, need to get some solid pipe since its currently 5.5" ss flex. I would do 5.5" flex -> 6" solid. I would need to use refactory cement on the joint between the two, and install a 6" damper like so: https://www.northlineexpress.com/6-cast-iron-stovepipe-damper.html

2) Keep it all the way closed, or slightly angled? Looks like some people kept it fully closed and even covered up the center hole to further restrict. Without covering any holes and leaving this in the closed position, do you know what kind of draft reduction it provides? And when you suggest even adding 2 key dampers, you would add both of them in a fully closed position for an even more significant reduction?

3) Do the keys need to extend outside of the faceplate, or can they be set and left alone, with no access unless you remove the face?

Also, thanks so much for all of the replies. This forum has been a huge help the past couple of months while I research what to do :)
 
Last edited:

stoveliker

Minister of Fire
Nov 17, 2019
7,261
Long Island NY
You need to extend the handle to where you can access it; during a cold start you may want to have it open to avoid smoke roll out when the chimney is not providing enough draft yet because it's not hot
 

bholler

Chimney sweep
Staff member
Jan 14, 2014
31,980
central pa
Installer said it's regency 106-130f

Google says that's a plate pilot reducer for the ci2601
I don't have a clue what they are talking about. But you don't have a pilot or orifice. It almost sounds like gas stove parts
 

north-east-colonial

New Member
Dec 9, 2022
27
North East, USA
I don't have a clue what they are talking about. But you don't have a pilot or orifice. It almost sounds like gas stove parts
See above link: https://www.hearth.com/talk/threads...0-fireplace-insert-risky-costly.132252/page-9

Looks like Regency calls the air intake a pilot/orifice, and people with the CI2600 talked about using them to restrict air.

And the part is listed here: https://www.kastlefireplace.ca/parts/regency/ci2601-hybrid-catalytic-wood-insert/10967/
 

bholler

Chimney sweep
Staff member
Jan 14, 2014
31,980
central pa

stoveliker

Minister of Fire
Nov 17, 2019
7,261
Long Island NY
I am surprised they can sell this; EPA testing asks for a minimum burn rate to avoid unnecessary pollution. And it does so with some standard (induced) draft that corresponds to the physics of a certain chimney height - hence the recommendation for chimney heights in most manuals.

Restricting the air flow would mess with that minimum burn rate, and I surmise invalidate the EPA approval...?
 

begreen

Mooderator
Staff member
Nov 18, 2005
99,755
South Puget Sound, WA
I did see another thread for the CI2700 where @begreen said all is good as long as the cat doesn't go above 1500.
That is a different context specific to the catalyst temperature. The dealer should put a manometer on the flue to measure the draft strength when burning and compare it to Regency's specified requirement. As noted, a 42' tall liner is exceptionally high and well beyond the tested design range.
Restricting the air flow would mess with that minimum burn rate, and I surmise invalidate the EPA approval...?
In the case of a very strong draft, the minimum airflow required for this burn rate may still be achieved though it might howl a bit going through a narrow orifice.
 

stoveliker

Minister of Fire
Nov 17, 2019
7,261
Long Island NY
In the case of a very strong draft, the minimum airflow required for this burn rate may still be achieved though it might howl a bit going through a narrow orifice.
I know, and I agree that it is best to get the system (chimney) up to mfg specs - but I know that e.g. BK can't and won't advise to use a key damper, because of legal issues as I outlined. Hence my surprise that Regency can sell a part that modifies the air on a stove (when other mfgs are even hesitant to suggest a part that only modifies the flue).
 

begreen

Mooderator
Staff member
Nov 18, 2005
99,755
South Puget Sound, WA
I know, and I agree that it is best to get the system (chimney) up to mfg specs - but I know that e.g. BK can't and won't advise to use a key damper, because of legal issues as I outlined. Hence my surprise that Regency can sell a part that modifies the air on a stove (when other mfgs are even hesitant to suggest a part that only modifies the flue).
Evidently, this is not as big an issue as it might seem. Some stove manuals recommend adding a damper in the flue for high draft situations. This makes sense. If the stove is getting too much air due to high draft then emissions might be exceeded, especially if the bloom of wood gases exceeds the secondary burn system or cat's ability to combust them.
 