Late "pop" of flame when fireplace is turned off

  • Active since 1995, Hearth.com is THE place on the internet for free information and advice about wood stoves, pellet stoves and other energy saving equipment.

    We strive to provide opinions, articles, discussions and history related to Hearth Products and in a more general sense, energy issues.

    We promote the EFFICIENT, RESPONSIBLE, CLEAN and SAFE use of all fuels, whether renewable or fossil.

Firegood22

New Member
May 3, 2025
2
Minnesota
I recently replaced the burner on my three sided LP gas fireplace. The install went fine and it starts and burns nicely; however, when I turn it off after several seconds there is a "pop" of flame in the back left corner near the air shutter (see video, wait for it, it takes a several seconds to appear). Is this anything to be concerned about? Ideas why it might be happening? I don't recall this happening with the burner I replaced. Thanks in advance.
 
I recently replaced the burner on my three sided LP gas fireplace. The install went fine and it starts and burns nicely; however, when I turn it off after several seconds there is a "pop" of flame in the back left corner near the air shutter (see video, wait for it, it takes a several seconds to appear). Is this anything to be concerned about? Ideas why it might be happening? I don't recall this happening with the burner I replaced. Thanks in advance.
View attachment 338627

Here is a post. It looks like unburned gases going off one last time.
 

Here is a post. It looks like unburned gases going off one last time.
That does sound like a similar situation. I’ll keep looking into it but sounds like something to not be too concerned about. Thank you.
 
This is common with LP burners. LP is dense so a bit of residual (rich) fuel sits in the bottom of the burner, and after the flow stops it will gradually mix with enough air to diffuse out and hit the pilot and then pop.
Is the unit sitting perfectly level? Sometimes if the burner is sloped away from the pilot it can make the issue more noticeable. But still it's not really anything to be concerned about.
 
Relatively common on LP burners, I've always referred to them as "Extinguishing pops". LP is heavier than air, so when the valve closes the gas still in the system can pool up a bit and ignite when it hits the pilot flame or other ignition source. It may also be lessened once the burner media - Logs, coals, rockwool - is installed.
 