I have been burning for three years. I always knew that maybe I didn’t have the best liner installed but when we first had the stove and liner installed I knew absolutely nothing about wood burning, stoves, and chimney setups. From this site I have learned that an insulated liner is key to a good burning experience. It seems most these days are installing flex liners as well.
So over time I have always known that the Installation I have may not be up to the best stands here but I did always figure that the installation was up to par to provide a safe burning experience. But now I have to second guess that.
We have a relatively new cinderblock with clay flue liner chimney system in our house that was purchased as a forclosure. It located central within the house. There is an upstairs flue and a down stairs flue (both separate and both clay lined).
The previous owners used a direct vent setup from the basement flue which is about 14x10inch or so. It is a very large clay lined flue. There was quite a bit of glazed creosote on the flue that we had swept off (it looked significantly clean after sweeping and could see most of the clay liner).
We purchased the stove from local store who used a licensed construction contractor to install almost all of their stoves. I had just started visiting this site and discussed with him installing a flex liner with insulated jacket. In his experience of 25 years installing chimneys he felt the flex liners were not as durable, and lesser quality than stainless steel liners and that the corrigations promoted creosote formation that brushes had difficulty getting. He also assured me that because we had a class A masonry chimney with clay flue liner in good shape that after sweeping the majority of the creosote out that he felt double wall or flex line was not necessary for an interior chimney. He seemed to make a good argument that the thicker SS rigid liner single wall would be ideal for longevity and durability.
So there is a 6 inch heatfab 304L Rigid stainless steel liner in place that is 25 foot approximately.
I sweep the liner every 3 months and get about 24-30oz of flakey ashy creosote for the past 3 years. So a total of 5 sweeps at this point. I just swept the chimney 2 weeks ago. Same situation.
Unfortunately I never checked AROUND the liner. The installer used some white batted insulation to block the top and bottom of the clay flue (kind of like a block off plate). The stove is 4.5 feet away from the chimney horizontally however and has a blockoff/pass through insulation wall that leads into the chimney. So I still don’t know if a steel block off plate is a necessity as the stove is 100% into the room it heats.
Well I swept the chimney 2 weeks ago and about 5 days ago an upstairs room that runs parrael to the chimney started to smell like some kind of burning. I run down to the chimney and see glazed black tar dropping from the side of the clay flue liner..NOT from inside the liner or even from the side of the liner. I used gloves and ran ALL the wood out of the firebox, shoveled all the coals out of the wood stove, shut it down. Called a different fireplace store, got a new chimney sweep recommendation and they came out today.
Here is where things get confusing for me.
The Chimney sweep claims that the entire chimney is black stove pipe. But clearly lables state it is stainless steel rigid liner. They say they don’t know what the installer was thinking installing black stove pipe for a liner….but I was like it says here it is a rigid stainless steel liner. He says nope its black pipe..??? But the sticker I showed him on the chimney says 6 inch heatfab 304L Rigid stainless steel liner.. I am kind of confused he doesn’t have a good answer.
The clean out T sits on the base of the fireplace (masonry). The new sweep says this is also not code. Probably as I have to prop the liner up with a wood block to get the T off so I can clean the flue out. When I do this the top of the liner pushes up at the top and the top block off plate is no longer on the top of the flue and therefore isn’t properly sealed at the top.
The chimney sweep runs a camera (his cell phone) down the liner. I just cleaned it and its immaculately clean. There are a few areas that look like possible rust? But you can’t really tell. There are also some areas that are screw holes that are visible without screws in them…But I’m not sure what is going on exactly.
The white insulation stuffed at the base of the chimney however is melted and turned into some weird hard candy like substance when sugar candy is made. Once it is pulled down you can see fluffy popcorn puffed creosote that is likely the chimney fire/creosote that caught on fire… but again this is all OUTSIDE the liner. The liner does move a bit and you can see some bends at some of the joints.. but it almost looks like the liner is lined by creosote now.
No obvious hole or disconnected site is seen. No obvious globs of creosote are noted dripping down the liner. It all appears to be collected along the old clay flue liner tiles.
I have called the installer. He is coming out next week to pull the liner and check it for problems. Then I am having the sweep company come out and both mechanically and chemically clean the liner. But I still don’t have a good answer as to WHY so much creosote is forming outside of the liner. The sweep company seems to want to blame it all on the use of BLACK STOVE PIPE but the Installer is pissed that they claim he installed black stove pipe when the stickers on it even say rigid ss liner.
He is still backing up his belief that I don’t REALLY need an insulated flex liner in an interior chimney and that rigid single wall ss is still ideal and more durable. He isn’t mad. He is going to pull the liner for free, but Its also pretty clear that unless I am missing something the sweep company doesn’t seem to be able to differentiate black stove pipe from stainless steel rigid lining? Or are they the same somehow?
Ultimately I feel I am going to need to get a 3rd opinion. I am sure I am going ot have to get a CSIA sweep out but there aren’t many in close proximity and the CSIA website referred me to a stove company who then referred me to a sweep who isn’t CSIA registered who came out and didn’t send the owner but a rather very young person who seemed to know what they were talking about. Except when I challenged them if the liner was SS.
I don’t know how smoke is escaping the liner which is the only possible way I can see for what is happening to occur. I will post pictures of everything I have.
1) Is my Heat Fab SS Rigid pipe SS or black pipe?
2) Code to have 6inch Rigid SS single wall in a class A Chimney that is 14x10inch?
3) Why is the liner clean but so much creosote forming OUTSIDE?!?! (Hopefully when the original installer pulls the entire liner we can get to the bottom of this better, but the cell phone down the liner didn't reveal anything other than a few screw holes...is this enough to do it?
4) Code to have the T clean out sitting on the masonry floor? The sweep seemed to feel this was a major problem.
5) 3rd opinion necessary? Neareast CSIA is about 40 miles away so It may be a pain to get them out.
6) any other questions you have for me you wish answered I would be more than happy to answer.
Again sorry for a long winded post. Just stressed, frustrated, ect. Not happy about the 300$ electric heat bills we will get over the next 2-4 weeks as we get this sorted out, but better than having a burnt down house.
So over time I have always known that the Installation I have may not be up to the best stands here but I did always figure that the installation was up to par to provide a safe burning experience. But now I have to second guess that.
We have a relatively new cinderblock with clay flue liner chimney system in our house that was purchased as a forclosure. It located central within the house. There is an upstairs flue and a down stairs flue (both separate and both clay lined).
The previous owners used a direct vent setup from the basement flue which is about 14x10inch or so. It is a very large clay lined flue. There was quite a bit of glazed creosote on the flue that we had swept off (it looked significantly clean after sweeping and could see most of the clay liner).
We purchased the stove from local store who used a licensed construction contractor to install almost all of their stoves. I had just started visiting this site and discussed with him installing a flex liner with insulated jacket. In his experience of 25 years installing chimneys he felt the flex liners were not as durable, and lesser quality than stainless steel liners and that the corrigations promoted creosote formation that brushes had difficulty getting. He also assured me that because we had a class A masonry chimney with clay flue liner in good shape that after sweeping the majority of the creosote out that he felt double wall or flex line was not necessary for an interior chimney. He seemed to make a good argument that the thicker SS rigid liner single wall would be ideal for longevity and durability.
So there is a 6 inch heatfab 304L Rigid stainless steel liner in place that is 25 foot approximately.
I sweep the liner every 3 months and get about 24-30oz of flakey ashy creosote for the past 3 years. So a total of 5 sweeps at this point. I just swept the chimney 2 weeks ago. Same situation.
Unfortunately I never checked AROUND the liner. The installer used some white batted insulation to block the top and bottom of the clay flue (kind of like a block off plate). The stove is 4.5 feet away from the chimney horizontally however and has a blockoff/pass through insulation wall that leads into the chimney. So I still don’t know if a steel block off plate is a necessity as the stove is 100% into the room it heats.
Well I swept the chimney 2 weeks ago and about 5 days ago an upstairs room that runs parrael to the chimney started to smell like some kind of burning. I run down to the chimney and see glazed black tar dropping from the side of the clay flue liner..NOT from inside the liner or even from the side of the liner. I used gloves and ran ALL the wood out of the firebox, shoveled all the coals out of the wood stove, shut it down. Called a different fireplace store, got a new chimney sweep recommendation and they came out today.
Here is where things get confusing for me.
The Chimney sweep claims that the entire chimney is black stove pipe. But clearly lables state it is stainless steel rigid liner. They say they don’t know what the installer was thinking installing black stove pipe for a liner….but I was like it says here it is a rigid stainless steel liner. He says nope its black pipe..??? But the sticker I showed him on the chimney says 6 inch heatfab 304L Rigid stainless steel liner.. I am kind of confused he doesn’t have a good answer.
The clean out T sits on the base of the fireplace (masonry). The new sweep says this is also not code. Probably as I have to prop the liner up with a wood block to get the T off so I can clean the flue out. When I do this the top of the liner pushes up at the top and the top block off plate is no longer on the top of the flue and therefore isn’t properly sealed at the top.
The chimney sweep runs a camera (his cell phone) down the liner. I just cleaned it and its immaculately clean. There are a few areas that look like possible rust? But you can’t really tell. There are also some areas that are screw holes that are visible without screws in them…But I’m not sure what is going on exactly.
The white insulation stuffed at the base of the chimney however is melted and turned into some weird hard candy like substance when sugar candy is made. Once it is pulled down you can see fluffy popcorn puffed creosote that is likely the chimney fire/creosote that caught on fire… but again this is all OUTSIDE the liner. The liner does move a bit and you can see some bends at some of the joints.. but it almost looks like the liner is lined by creosote now.
No obvious hole or disconnected site is seen. No obvious globs of creosote are noted dripping down the liner. It all appears to be collected along the old clay flue liner tiles.
I have called the installer. He is coming out next week to pull the liner and check it for problems. Then I am having the sweep company come out and both mechanically and chemically clean the liner. But I still don’t have a good answer as to WHY so much creosote is forming outside of the liner. The sweep company seems to want to blame it all on the use of BLACK STOVE PIPE but the Installer is pissed that they claim he installed black stove pipe when the stickers on it even say rigid ss liner.
He is still backing up his belief that I don’t REALLY need an insulated flex liner in an interior chimney and that rigid single wall ss is still ideal and more durable. He isn’t mad. He is going to pull the liner for free, but Its also pretty clear that unless I am missing something the sweep company doesn’t seem to be able to differentiate black stove pipe from stainless steel rigid lining? Or are they the same somehow?
Ultimately I feel I am going to need to get a 3rd opinion. I am sure I am going ot have to get a CSIA sweep out but there aren’t many in close proximity and the CSIA website referred me to a stove company who then referred me to a sweep who isn’t CSIA registered who came out and didn’t send the owner but a rather very young person who seemed to know what they were talking about. Except when I challenged them if the liner was SS.
I don’t know how smoke is escaping the liner which is the only possible way I can see for what is happening to occur. I will post pictures of everything I have.
1) Is my Heat Fab SS Rigid pipe SS or black pipe?
2) Code to have 6inch Rigid SS single wall in a class A Chimney that is 14x10inch?
3) Why is the liner clean but so much creosote forming OUTSIDE?!?! (Hopefully when the original installer pulls the entire liner we can get to the bottom of this better, but the cell phone down the liner didn't reveal anything other than a few screw holes...is this enough to do it?
4) Code to have the T clean out sitting on the masonry floor? The sweep seemed to feel this was a major problem.
5) 3rd opinion necessary? Neareast CSIA is about 40 miles away so It may be a pain to get them out.
6) any other questions you have for me you wish answered I would be more than happy to answer.
Again sorry for a long winded post. Just stressed, frustrated, ect. Not happy about the 300$ electric heat bills we will get over the next 2-4 weeks as we get this sorted out, but better than having a burnt down house.